Is this one of those big modular hotels where the entire bedroom is craned into position and "plugged in"?
I'm thinking its a big concrete or metal box. A fire within the room or the CU would be confined to the module itself. The hole in the plasterboard doesn't go through to the rest of the hotel.
No
 
In a commercial premesis it is marked as a C2 in the Napit codebreakers book.
They also code 2 pvc cables not rcd protected in walls less than 50mm from surface so it’s not to be taken as gospel in my opinion.
Books like this can have the opposite effect as in people will use it as gospel rather than coding it on the current circumstances
 
Thinking about the hole I would not code 2 for fire reasons because as long as all the terminals are tight its not going to catch on fire , but might code 2 it due to the amount of dust debris that could build up inside the CU and get into the terminals due to the large hole.
Again reading the napit codebreakers book it states holes not made goot as to reduce the spread of fire are C2. I would rather C2 and have a valid reference such as a book than to C3 it and argue against it.
 
Again reading the napit codebreakers book it states holes not made goot as to reduce the spread of fire are C2. I would rather C2 and have a valid reference such as a book than to C3 it and argue against it.
You have bs 7671 as reference.
It can be considered a C2 if it’s a fire barrier as per section 527
 
Thinking about the hole I would not code 2 for fire reasons because as long as all the terminals are tight its not going to catch on fire , but might code 2 it due to the amount of dust debris that could build up inside the CU and get into the terminals due to the large hole.
Again reading the napit codebreakers book it states holes not made goot as to reduce the spread of fire are C2. I would rather C2 and have a valid reference such as a book than to C3 it and argue against it.
Napit are wrong then.
I disagree. If someone was to plug something in
You have bs 7671 as reference.
It can be considered a C2 if it’s a fire barrier
527.2.1 is the reg attached to the coding in the napit book. Obviously there will be no mention of coding in the regs but again i would rather have a reference, although i agree not gospel.
 

Reply to Poor install EICR 12 year old hotel in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
360
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
All - Would appreciate some advise or professional help as I'm facing a £4.5K bill following an EICR which seems to highlight issues that passed...
Replies
21
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock