I think most reports of smart meters tripping RCD's were a little bit more frequent than that, often every 24 hours.

Time to find/call a sparks who will very quickly be able to see how close the RCD is to tripping 'normally' and if high track down why.
If this leads nowhere, then there are a couple of Memera2000 main switch isolators on ebay at the moment for under a fiver. You could suggest a sparks temporarily replaces the RCD with one and powers the RCD separately as this would prove the point if it's the meter doing it.
Had OVO/SSE engineer attend today. He intended to replace the smart meter with 2nd generation as he was going through the commission process the Garage breaker tripped and wouldn't reset. Nothing on in garage or plugged in. He explained there are several types of breakers that the 2nd generation nuisance trips cause by the radio waves. Proteus boards being one type. He said he would re-install the original after 'the fix' tin foil didn't work. End result I no longer have smart meter connectivity because the original was no longer connected to DCC. Waiting to hear from OVO again.
 
Had OVO/SSE engineer attend today. He intended to replace the smart meter with 2nd generation as he was going through the commission process the Garage breaker tripped and wouldn't reset. Nothing on in garage or plugged in. He explained there are several types of breakers that the 2nd generation nuisance trips cause by the radio waves. Proteus boards being one type. He said he would re-install the original after 'the fix' tin foil didn't work. End result I no longer have smart meter connectivity because the original was no longer connected to DCC. Waiting to hear from OVO again.
Which board is the garage breaker on? Or is that on a board that hasn't been photographed yet?

I'm trying to decide if there was a genuine problem with his new meter and a Proteus device, or he somehow mixed up the tails and that was the cause of an RCD objecting.

As 7 months have now passed it might be worth considering getting the whole install tidied up from the meter tails onwards and a new modern consumer unit fitted.
This smart meter radio interference thing only affects older consumer units and devices in my experience. I've not known it happen with anything fitted in the last 5-10 years.
 
Which board is the garage breaker on? Or is that on a board that hasn't been photographed yet?

I'm trying to decide if there was a genuine problem with his new meter and a Proteus device, or he somehow mixed up the tails and that was the cause of an RCD objecting.

As 7 months have now passed it might be worth considering getting the whole install tidied up from the meter tails onwards and a new modern consumer unit fitted.
This smart meter radio interference thing only affects older consumer units and devices in my experience. I've not known it happen with anything fitted in the last 5-10 years.
My post is not about the original case, it was my experience yesterday. Prior to the second generation install the generation 1 meter had no issues. According to the engineer it was a radio wave issue identified as affecting certain types of RCD. As for the board, it was just one consumer unit. The garage breaker is an RCCB that has had no previous issues. Seems once again the second generation we were promised was the solutions to drop outs etc isn't. Now there is a third type supposedly available next year. Meanwhile our smart meter is no longer connected to DCC
 