Basically I have got my 301 unit 1 exam next week, and there is this question bugging me in one of these practice mock exams.

Please help, but using the formulas and letters used in the 2330 c+g so I remember it for the exam.

Qst: A capacitor of 100uf is connected in parallel with a 20ohm pure resistor. The group is connected to a 200v 50hz supply. Calculate the power dissipated in the combination.

a.2000w
b.2400w
c.3000w
d3600w

and my teacher said the answer is A. 2000w

What I thought you do:

xc = 1/ 2π x 50 x 0.0001= 31.8ohms

Then add the 31.8ohm reactances to the 20ohm resistor (in parrellel) ....
1/ 31.8 + 1/ 20 = 12.28ohms

Now I have the resistance and the voltage is given so I = V/R =16.29a

and to answer the question, P= V x I (200 x 16.29= 3258watts)

I really can't think of where I am going wrong, I think it something with the way I am add the reactance and resistance together :s
 
hi, i struggled with this one too, tutor told me that there is no power in capacitor/inductor, (maybe someone with a bit more knowledge could explain why),
the answer is a 2000w

I=v/r= 200/20 =10a
p=IxV = 10x200 = 2000w

hope this helps
 
hi, i struggled with this one too, tutor told me that there is no power in capacitor/inductor, (maybe someone with a bit more knowledge could explain why),
the answer is a 2000w

I=v/r= 200/20 =10a
p=IxV = 10x200 = 2000w

hope this helps

I f'ing knew that cap/iduc use 0watts too! (Just forget on this question :confused:)

So yes, I think you just do what I did, but don't add the reactance with the resistance and just use the 20ohms

cheers pal
 
it catches me out sometimes with how the Qs are worded, had my 301 exam last thursday, passed , a lot of Qs on motors in the exam
all the best for next week

motors is probs my weakest area. All the formulas I seem to remember. But with the motors there seems to be loads: ac,dc,3phase...then loads of different ones within these 3! and remembering how to reverse the rotation or what components each has! nighmare mate. But well done on your 301
 

Reply to power dissipated in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Question: Three coils of resistance 40 Ω and inductive reactance 30 Ω are connected in delta to a 400 V 50 Hz three phase supply. The total power...
Replies
20
Views
2K
Hi guys, hopefully, maybe, someone will be able to help me with this one. Trying to get my head around true power calculations and am really...
Replies
18
Views
2K
Doing my assignment for Three phase motors and one of the questions is for Torque. The assignment is due on Wednesday and I had the assignment...
Replies
0
Views
2K
K
a capacitor of 100uf is connected in parallel with a 20ohm pure resistor. the group is connected to a 200v 50hz supply calculate the power...
Replies
4
Views
3K
lee sandland
L
E
Would very much appreciate some feedback from experienced PAT testers on this topic. It has been raised previously but I don’t believe it’s been...
Replies
3
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock