Hi Tel.
I quite agree that the duration of the fault is set by the resistance of the fault path and the characteristics of the OCPD. Hence why we measure Zs.

Now, "a line/earth fault will cause the potential of the earthed component to rise to line value, at the point of the fault".

Well, yes, except that a line/earth fault also drags down the line voltage at the point of the fault; so the local line voltage is reduced. So, say for example, the line and earth parts of the fault path are of equal resistance, then the voltage at the fault will be half the supply voltage. In effect, the resistance of the two parts of the fault path form a potential divider across the supply.

Or am I misunderstanding?
 
In a healthy circuit, the line and neutral have similar if not equal resistance.
Would this combined resistance halve the supply voltage?
In many instances, the CPC has a smaller CSA than the live conductors, as such some volt drop would be expected, but not by a significant amount.
In many cases where an earth fault occurs, the neutral is still connected.
In such cases, the CPC would become a parallel conductor with the neutral, as such reducing resistance.
 

Reply to Protection by RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
926
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Can anyone tell me the latest regulation for RCD protection on socket outlets, I believe it's required for sockets up to 32A but I'm told it...
Replies
4
Views
2K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
677
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
627

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock