Yes, I do it on every annual assessment and you're confirming supply polarity at the same time.
 
Think if you tested on the incomming side of the main switch and you had no voltage, then surely you'd realise your test was dead anyway or theres a power cut in the areaLOL
 
If the lamp fails to light on the outgoing side of the main switch you should then prove the tester, ie it should light on the incoming side (or in a proving unit).
If it doesn't, either your test lamp is broken, or as already metioned, there's a power cut.
 
Can you use main incoming L&N as known voltage source instead of a proving unit?

Never seen a proving unit and certainly never owned one

There is no better way of first proving your meter actually works than by shoving it onto the national grid
Then theres no better way of deciding a circuit is live or dead, than by using that same meter to give you many more days of sparking without burning those pinkies :)
 
A proving unit lights up if working. I guess if you wanted to Mr health and safety you could argue using the incoming main to do an initial proving could be classed as 'Live working' and classed as unnecessary as other means available, and secondary testing for voltage is necessary to prove isolation..Food for thought
 
if you are doing the ze test you have no choice then to work live so you might as well do the proving at the cu when testing for a dead cu to perform r1r2 tests ect.

edit my proving unit don't light up, my voltage tester dose.
 
if you are doing the ze test you have no choice then to work live so you might as well do the proving at the cu when testing for a dead cu to perform r1r2 tests ect.

edit my proving unit don't light up, my voltage tester dose.

My proving unit has no 'lights' either!
 
I have a proving unit but mostly use whatever is available and close, the idea is to "prove" your tester is working, if it doesn't come on when you expect it to then you have to get something else to test that supply with, even if that supply is your proving unit. Meter tails are great but if my Martindale said they were dead I'd still check them out again with something else before I got hold of them. It's about safety so you have to "prove" your tester before and after you test something is dead. The book says with a "known" supply, you only "know" its a supply if the tester comes on.
 
So if you're up for assessment, and you're working on a CU, and you have to hand a readily available 'known source'. But if you don't own a proving unit, is the assessor going to say 'what happens when you're not at the CU, how will you prove dead if you don't own a proving unit?'?
 
Mate all testing equipment needs to be calibrated, and proved with a certificate.

In my many years in this business I have never calibrated or been asked to calibrate a proving unit, nor can I find any requirements to calibrate!

Of course the calibration companies will provide this service if asked, in return for £40 or £50 but then again, they'd probably calibrate a Thermos Flask if you requested it.
 
You do not require a proving unit if you follow the safe isolation procedure.

After identifying circuit to work on you test your tester on a known supply (This can be the incomming tails before isolation, a proving unit or a different circuit). If all LED's light up you know it is working so you then test the supply you have isolated.

If correctly isolated, no LED's will light up!!!

Then re-test you tester on known supply (to check all LED's are still working and it hasn't died between proving and checking isolation) if all LED's light up, then you know the isolated supply is dead.

This might be usefull here : http://www.esc.org.uk/pdfs/business-and-community/electrical-industry/BPG2_09.pdf

Check out page 13

Cheers guys
 
In my many years in this business I have never calibrated or been asked to calibrate a proving unit, nor can I find any requirements to calibrate!

Of course the calibration companies will provide this service if asked, in return for £40 or £50 but then again, they'd probably calibrate a Thermos Flask if you requested it.

Well although no requirement to under BS 7671, 612.1 refers to requirements, and best practice and common sense would say you should...

http://www.esc.org.uk/pdfs/business-and-community/electrical-industry/BPG7_10.pdf

Also this clip from DIS registration from NICEIC...

A check of test instruments and leads used for
certification purposes. As a minimum, the business
needs to have access to instruments to provide
voltage indication and to test insulation resistance,
continuity, phase/earth loop impedance and residual
current devices. You should have records to
demonstrate that a system is in place to ensure the
accuracy and consistency of test instruments used
for certification purposes. These will need to be
available for inspection. An example leaflet is enclosed
with this pack.

http://niceic.com/Uploads/File2368.pdf
 
I have a copy of that form but it doesn't call for monthly or any other such checks on a proving unit does it?
 
IQ I misread you OP I thought you said no test equipment needed calibration I apologise.

100 Lines...

must read slower
must read slower
ATB Steve
 
IQ I misread you OP I thought you said no test equipment needed calibration I apologise.

100 Lines...

must read slower
must read slower
ATB Steve

I thought it was weird that you were persisting with it! :)
 
never owned a proving unit, and never had to show safe isolation at any assesment. Flick the main switch off and the lights go out! usually enough proof for me to start work on a domestic CU.
 
never owned a proving unit, and never had to show safe isolation at any assesment. Flick the main switch off and the lights go out! usually enough proof for me to start work on a domestic CU.

:)


Thats sure to make the health and safety brigade squirm
The knuckle wrapping will soon begin :)
 
So if you're up for assessment, and you're working on a CU, and you have to hand a readily available 'known source'. But if you don't own a proving unit, is the assessor going to say 'what happens when you're not at the CU, how will you prove dead if you don't own a proving unit?'?

I have a Fluke T120 Voltage/Continuity Tester and my proving unit is a couple of 9 volt batteries in a plastic box with terminals attached to two bolts (screws) showing out (yes, you got the idea) - a cheap & cheerful proving unit.

Works wonders every time!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Peterborough

Thread Information

Title
Proving dead at the CU
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
30

Advert

Thread statistics

Created
ringer,
Last reply from
Goody,
Replies
30
Views
5,646

Advert

Back
Top