Can you use main incoming L&N as known voltage source instead of a proving unit?
I wouldn't as what if your test lamp said it was dead and it wasn't because you have a duff test lamp?
Can you use main incoming L&N as known voltage source instead of a proving unit?
if you are doing the ze test you have no choice then to work live so you might as well do the proving at the cu when testing for a dead cu to perform r1r2 tests ect.
edit my proving unit don't light up, my voltage tester dose.
Mate all testing equipment needs to be calibrated, and proved with a certificate.
In my many years in this business I have never calibrated or been asked to calibrate a proving unit, nor can I find any requirements to calibrate!
Of course the calibration companies will provide this service if asked, in return for £40 or £50 but then again, they'd probably calibrate a Thermos Flask if you requested it.
IQ I misread you OP I thought you said no test equipment needed calibration I apologise.
100 Lines...
must read slower
must read slower
ATB Steve
never owned a proving unit, and never had to show safe isolation at any assesment. Flick the main switch off and the lights go out! usually enough proof for me to start work on a domestic CU.
Thats sure to make the health and safety brigade squirm
The knuckle wrapping will soon begin![]()
Thats sure to make the health and safety brigade squirm
The knuckle wrapping will soon begin![]()
So if you're up for assessment, and you're working on a CU, and you have to hand a readily available 'known source'. But if you don't own a proving unit, is the assessor going to say 'what happens when you're not at the CU, how will you prove dead if you don't own a proving unit?'?