An the answers 3 and 4 are wrong.

Think about how the earth leakage part of the rcbo works.
 
Ok, Peter lets add on to what 44ALLAN said.

If we as sparkies generally deal with two types of fault, one would operate a MCB and the other an RCD, what faults would you be looking for?
 
When less current comes back from what was put out, this suggest some current has leaked to earth causing an out of balance flux
 
When less current comes back from what was put out, this suggest some current has leaked to earth causing an out of balance flux

Ok if your saying an earth fault?
Go back to your original post and tell me if there are any 'earth faults' in the answers:)
 
A) Line to Earth Fault of approx. 2.3Ω RCD portion would operate as it is faster than either thermal or magnetic portions of the device

B) Line to Neutral Fault of approx. 0.01 Ω MCB Thermal would likely operate first as this should be faster than magnetic on this type of fault, but quality and condition of the device will determine

C) Neutral to Earth Fault of negligee impedance RCD would operate due to the imbalance across the toroid detection circuit

D) An overload of approx. twice the nominal rating of the device MCB Thermal should operate first in this type of fault, but again depending on the quality and condition of the device the Magnetic may get their first, this will also be determined by the duration of time taken to reach peak tripping current for the device. Slow overload may operate magnetic first, fast will almost always operate thermal first.

Hope that helps.
 
A and C are earth faults :-), justifying the question is the hard part for me, can I say they trip through the RCD part of the RCBO as they are earth faults
 