My recommendations:
Install new Earth Electrode!!!!
Install Gas Bonding
Install new CU
Cant recommend anything with regards to circuit 6 at present as could not identify any particular fault
Oxygen machine - one tactical solution would be to run a non-RCD Protected circuit for this, dedicated for that machine.
Can you check they are all definately class two? Have you checked they are wired correctly in the plug top.
as already said check things other have suggested. Something will show up as an alert!
oxygen Machine is standing out as an odd one to me though.....
could be a duff RCD. ramp it.
I recommended further investigation after main issues sorted - no earth and replace CU (which will replace the up-front RCD)
Oxygen machine was plugged into another circuit and worked fine - machine PAT Tested on site all clear - no earth in plug so only IR and visual check - all passed fine
Im wondering if the lack of earth (only through the water pipe) could cause the RCD to trip, but dont know how considering this gave an earth of 12ohms with is better than most earth rods
whats also wired is with MCB 6 just turned off, the RCD held fine - where if this was an N/E Fault then the fault current would travel from other circuits (cooker, kitchen sockets, IH, electric shower, etc) and pass down the N conductor and back through the earth conductor to water pipes and generate >30mA and trip
Do you know how a RCD actually works?
it monitors for a imbalance in current between the two live conductors, it has nothing to do with the earthing arrangement of the property.
Yes I know exactly how RCDs work - but I also remember something about 30mA RCDs dont work correctly at a certain resistance - but cant remember much on it as I always makesure I get an earth of less than 100ohms
Well find the information you are referring too, then have a look and see if it will affect the RCD in this instance. Personally I would say there is still a load connected somewhere that is causing the problem.
i agree.
My recommendations:
Install Gas Bonding
Install new CU
what sort of nic os the service head in?
lol ! this thread is absolutely all over the place !
no earth but no mention of whether its tns tnc tt ,etc.
and you'd have to be a complete loon to even contemplate rcd protection for any home based medical equipment , thats what the regs exemptions are for.
and the fact the OP thinks 6 sockets on a radial is cause for concern is rather worrying in itself.
and fitting a new CU is hardly going to make all the problems dissapear is it ?
whats needed is a more structured approach to assessing each defect whilst remaining within the customers instructions & budget.