Far too sensible as usual Biff ;-)
I'd agree, sensible. However there'll be some situations where home medical equipment has to be on an RCD. The obvious one is on a TT supply with the typical Ra readings, where you can't avoid using an RCD for earth fault protection. Also, if the equipment is portable and may be used in a variety of locations, then it would be hard to justify not RCDing the socket circuit. If used in one location I'd put in a non-RCD radial for one labelled socket.
If the equipment is life-critical, then a UPS is the obvious solution, especially as tripping RCDs are not the only reason for mains failure.