Head scracter.

If your dead tests are good

Does the RCBO test OK at 5 & 1 times.

When you do switch on the RCBO and then the lighting cct I take it that the RCBO does not see a imbalance. I take it you have switched the lights on and off and tested a load on the sockets making sure it holds?
 
Are there any other existing circuits on the board that you have put these on? If so, have you tested IR on these circuits? I know that it shouldn't be relevant but RCBOs are only single pole, any N - E short could be causing it to behave strangley. Maybe clutching at straws here............but it's worth a look.
 
As it's a TT system, I'm guessing the MCB is covered by it's own RCD. Are you 100% certain the RCBO hasn't been installed in some way incorporating the RCD's neutral supply?
Is the RCBO neutral completely independant of the MCB (RCD) neutral?
 
Pretty much what Ponty just said. Got a photo of your board? My money's on a dodgy neutral connection at the board.
 
I don't think your installation is contravening regs as long as you are satisfying 543.1.2
I was thinking along the lines of Ponty for the cause of the fault?
 
I don't like the idea of a single earth being split for 2 circuits. Unless it's made clear where the JB is and where it is connected, you'll cause a headache for some poor spark in the future I'm sure.

I'm now thumbing through the regs to see if I can back this up. If it's deemed satisfactory to do it, fine. I just personally don't like the idea.
 
so your ZE is 54 Ohms ??

Thats very high. I think thats your problem.

Need to get your ZE below 21 Ohms

Sav
 
You should label the earth connection and state is supplies two circuits as someone might come along and disconnect one of the circuits and think its the earth and voila!! Circuit without earth and someone shocked...
Sharing 2 circuits with one CPC is not the best practice imho.
 
Another negative vote for combined earth.

If isolating the MCB allows the RCBO to be reset, it must be that the MCB live is causing an inbalance in the rcbo cct by induction.

My next move would be to temporarily swap the cct connections at the Mcb / Rcbo, so the sockets are on the Rcbo and lights on Mcb and repeat the test, it may be a peculiarity of how the cable cores are layered.

I think you'll end up using 2 cables tho'
 
I don't like the idea of a single earth being split for 2 circuits. Unless it's made clear where the JB is and where it is connected, you'll cause a headache for some poor spark in the future I'm sure.

I'm now thumbing through the regs to see if I can back this up. If it's deemed satisfactory to do it, fine. I just personally don't like the idea.

A common cpc between circuits is acceptable as long as it meets the requirements of all circuits, size wize etc
 
so your ZE is 54 Ohms ??

Thats very high. I think thats your problem.

Need to get your ZE below 21 Ohms

Sav
Where does 21 Ohms come from? I've only heard of 200Ohms for TT system being "acceptable". Not come across the 21 ohms figure before?
 