R

Robinson

Hi Guys, Looked at a job today. Basement flat. CU Has a Circuit feeding a small CU in the upstairs shop
cable is a 16mm T&E on a 40 amp mcb. Rest of circuits on RCBO's.
Question is Should this cable feeding shop be RCD protected? Does this become commercial?
The Board in the shop is RCD protected.

SO its just the supply cable itself that is not. which is coming from a domestic environment.
i note though the cable comes out of board in flat straight through ceiling into shop..

any thoughts
 
There is absolutely no point in RCD protecting a lone cable, in my opinion. Also, were you too, you'd have a very expensive discrimination problem to solve as you'd need a 40A S type, and that won't be cheap.
 
Is the cable protected by trunking,if so not needing rcbo.

Even if it isn't, you don't need to RCD protect a distribution circuit with a 5s disconnection time. The FINAL circuits are protected, according to the OP, which is quite (probably) correct.
 
I'm assuming that the cable is concealed in a wall, and there is no other acceptable method of additional protection.
As such (again an assumption) the OP is asking whether the exception to the requirement for RCD protection due to the installation being under the control of a skilled or instructed person is applicable.
 
cable goes through ceiling (from top of FLATS CU). straight up into a TRUNKING then trunk all way to board (In Shop). Shop has very very small load. few sockets and 2 strips. And under operation of skilled person, its going to be a little store room..with a little man.

Rockit: Yes Rcd s typre $$$$$$ agreed.

Yes Final circuits are protected RCD.
This a 16mm Distribution we are talking about. On a Domestic CU 40amp breaker, feeding Commercial Stores.
 
If run in trunking then sounds like no need for any additional protection.

What are the chances of the flat being under the supervision of a skilled or instructed person? In other words, if buried in the wall at<50mm the RCD needed.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCBO Or No RCBO that is the question
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
Robinson,
Last reply from
Robinson,
Replies
10
Views
3,507

Advert