tbs1983
If for example its a lighting circuit I would go to end of line and carry out earth loop test, and following that I would do RCD test at same place. 1/2 current test 1st which shouldnt trip RCD, then 1x current, then 5x current. I understand the 0 and 180 methods as it accounts for both sides of the AC waveform, but to be honest its not something ive ever done and I would guess a lot would say the same.