Discuss RCD Aways tripping in the UK Electrical Forum area at ElectriciansForums.net
Douglasmcc
I'm new to this forum. I've recently done a visual inspection of a campsite hall as a favour which has has had an extension built. It's all a bit of a mess electrically speaking. The consumer unit has a 100A main switch and 10mcbs divided across the two 30mA RCDs. The major problem is that when a significant load is placed on circuits 2 & 3 it trips the RCD2 of the other side of the board, not its own. The consumer unit circuits:
RCD 1 - 63A 30mA
  1. External Socket (40A)
  2. Socket, hand dryers, Shed & Gas Boiler (32A)
  3. Hall sockets (32A)
  4. Fire Alarm (16A)
  5. Hall lights & outside lights (6A)
RCD 2- 63A 30mA
  1. Kitchen Sockets (32A)
  2. External socket (32A)
  3. Gas isolator and fly zap (16A)
  4. Hall lights (6A)
  5. Kitchen & toilets & emergency lights (6A)
My initial observations:
My guess in regards to the tripping is that the neutral has been crossed over causing an imbalance between the two sides of the board?
The division of circuits above is not particularly intelligent and not how I was taught; divide the board between fixed and portable circuits.
There are two 13a spur units sitting about 20cm above a stainless steel wash hand basin. I'm sure this is not safe?
There is no earth bonding at all throughout the building especially in the kitchen, which has stainless steel sinks and tables. Nor is any bonding visible in or around the hot water tank or the gas boiler. The SWA cable earth tag has not been fixed to the consumer unit, although it is present.
I'd appreciate your input especially regarding the tripping.
Many thanks
almost certainly a neutral problem. either as davidM said, or some other shared/crossed N.
Agree re neutrals. Spurs need moving looking at zoning. Maximum demand seems to exceed main fuse. I would suggest to the people to get back the contractor who installed and discuss the matters. Is there a cert. for it all to look at? Looks like it trips when 2 and 3 load up, they are both rings so maybe swapped neutral there?
The spurs though not ideal, may not be a code 1 or 2 (if you read the description guides for the codes and then check with the regs for zoning if applicable, you can determine what code you feel is adequate, for this situation)
Supplementary earth-bonding is not always required, a simple test to determine this can be carried out. Main earth bonding is required for all incoming services that are conductive (i.e - aluminium, steel, copper, lead etc..) if you check the regs it is all explained in there.
Hi - the observed SWA termination concerns me. Is it a metal CU, is the SWA relied upon for installation earthing? Perhaps confirm Ze and a few Zs ?
You are right about outlets over a sink. Outlets should be min 300mm to the side of a sink with the aim of reducing water splashes onto them. To me, these need to be relocated. Maybe the outlets were there before the sink was added :)
Because everyone (wrongly) used to do it without a second thought. If it's metal bond it! Some say this is why the character Jaws from James Bond never used to smile - fear of having his teeth bonded?!
I don't do EICR's, as I feel my level of experience would not enable me to scrutinise an installation to the correct degree. And I do not wish to take additional responsibilities at my age :). I also do not wish to have the additional indemnity insurance, although I expect that would be an additional few pounds a month.
However, with just a few lines from the OP, bonding metal tables, bonding hot water tank etc, I would just question his experience in carry out an EICR, if infact that is what is doing.
OP, not having a go at you and we are all can learn from each other, but do you think you should be doing this sort of work on your own, with your current level of expertise? If things do go wrong, your insurance might not protect you. Just saying.
Can't see any reason for supplementary bonding. Division of circuits across rcds seems fine to me. What is this zoning business? The hall lights are hall lights not a hallway. It is almost certainly crossed neutrals though.
Reply to RCD Aways tripping in the UK Electrical Forum area at ElectriciansForums.net
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...