This reads plain to me but a few are not reading the OP properly ...
At mains there is a 3ph board with 100mA rcd main switch
Also a 1 phase supply straight of the meter via a henley block to a sw/f + RCD ...lets assume 100mA
When a fault trips the rcd of the 3ph board the rcd IN THE house trips so assuming a 30mA is tripping in the house possibly 17th edition board....
can the OP confirm this!?
Thats how I read it as well ...
I thought I had read it right, what I thought was, "what is protecting the single phase supply"? it is from henley blocks to a switch fuse then to the house where there is a rcd?? or does he mean there is a rcd in the barn at the supply, oh dear I am now getting confused too
Where abouts is the suppliers transformer ...is it close up a pole?
What kind of rcd's are they - are they modern type that measure inbalance between L/N?
Have you ensured all your customer side connections are sound and tight... check busbar tabs are on the correct side of any mcb, rcd and main switch terminal clamps.
rcds/mcbs are mem old 3871/4293 type, dunno about house end ive not been able to get access in there yet but assuming they are of similiar age
also not sure of tx location
When a fault trips the rcd of the 3ph board the rcd IN THE house trips so assuming a 30mA is tripping in the house possibly 17th edition board.... can the OP confirm this!?
Edit confirmed in post 15.
Spot on darkwood yes 100mA s type sp protecting submain(this is holding fine but the 30ma rcd in house is tripping out with the 3pn board in the barn)
Now we have the correct set-up as confirmed in my post 13 any chance the OP can answer y questions way back in post 2 :juggle2: ill just wait then!!
head scratcher alright, but I think I would be eliminating any N-E faults on both installations in the absence of any better ideas. N-E faults do funny things to RCD's.......
You need access to the house , to confirm what RCDs are there and earthing arrangements at the house,,,
well certainely a headscratcher alright, seems very strange, maybe the fact both supplys connect to the rod and the fact a surge to earth trips the one may mean the other is over sensitive, must admit it is a funny situation which I am struggling with at the moment.
La de da da da ....any chance of responding to post 2 yet its getting further away as we speak... might be using the 18th edition by the time you respond to it :juggle2:
Please refer to post 21 for guidance.
Welchyboy1 however everytime there is a fault on the barn distribution board and its main rcd operates it takes out the rcd at the farm house too any ideas?[/QUOTE said:
A strange one indeed .
first thing to do would be confirm this is actually happening with test meter .
you know how customers can somehow get the wrong end of the stick .
It is a pain
im thinking of isolating the two earthing systems from each other, having a rod for each and insulating the SWA sheath at the house end from the barn see what happens
just wanted a few ideas for when i get back there
Ramp test the house RCD