If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Farm job im at has a problem


three phase tt system comes into main barn area, three phase main distribution board (with 100mA s type 4 pole rcd as main switch) supplying barns and general farm buildings

Swa single phase supply to farm house(around 40meters away), supplied directly from meter side of distribution board on henly blocks to switchfuse/rcd

so house supply is totally independent from the barn supply

however everytime there is a fault on the barn distribution board and its main rcd operates it takes out the rcd at the farm house too

i havent been over to the farmhouse yet but i cant understand why it would be knocking out the rcd in the house?

any ideas?
 
Where abouts is the suppliers transformer ...is it close up a pole?
What kind of rcd's are they - are they modern type that measure inbalance between L/N?

Have you ensured all your customer side connections are sound and tight... check busbar tabs are on the correct side of any mcb, rcd and main switch terminal clamps.
 
If the SP supply is taken from the load side of th e TP RCD the any fault on the SP supply will trip the TP RCD
 
If the SP supply is taken from the load side of th e TP RCD the any fault on the SP supply will trip the TP RCD

He's explained the set-up and the house supply is independent from the 3ph supply and straight off a henley block from the meter.
 
  • Like
Reactions: 2 people
As I read it Pete the house SP supply comes off before the 3P RCD so they should not effect each other. Which is the problem the OP is trying to get a handle on as to why they actually are!
 
  • Like
Reactions: 1 person
If theres a single earth stake in use for both barn and house , and all bonding is done at the house , it could be the Ze of the earth stake is higher resistance than the bonding at the house and fault currents are back fed to house , just a thought,,
 
Time to sit back and watch (read) you guys are just out thinking me! Far too fast for my simple brain processing ability ......
 
Sorry lads too much red stuff missed that apologies for the assumption
 
  • Like
Reactions: 1 person
This reads plain to me but a few are not reading the OP properly ...

At mains there is a 3ph board with 100mA rcd main switch
Also a 1 phase supply straight of the meter via a henley block to a sw/f + RCD ...lets assume 100mA

When a fault trips the rcd of the 3ph board the rcd IN THE house trips so assuming a 30mA is tripping in the house possibly 17th edition board.... can the OP confirm this!?


Edit confirmed in post 15.
 
he said henleys, switchfuse, rcd.

then i hear TP board and TT the first thing i think of, is the first (RCD) enclosure insulated?
 
so it is a TT system, what is protecting the sub main to the house :lipsrsealed2:

100ma sp rcd, at barn end, i haven't been into the house yet but from what the customer describes a 30ma rcd covering her whole cu and this is whats tripping out
 
  • Like
Reactions: 2 people
This reads plain to me but a few are not reading the OP properly ...

At mains there is a 3ph board with 100mA rcd main switch
Also a 1 phase supply straight of the meter via a henley block to a sw/f + RCD ...lets assume 100mA

When a fault trips the rcd of the 3ph board the rcd IN THE house trips so assuming a 30mA is tripping in the house possibly 17th edition board....






can the OP confirm this!?






Thats how I read it as well ...
 
I thought I had read it right, what I thought was, "what is protecting the single phase supply"? it is from henley blocks to a switch fuse then to the house where there is a rcd?? or does he mean there is a rcd in the barn at the supply, oh dear I am now getting confused too
 
Where abouts is the suppliers transformer ...is it close up a pole?
What kind of rcd's are they - are they modern type that measure inbalance between L/N?

Have you ensured all your customer side connections are sound and tight... check busbar tabs are on the correct side of any mcb, rcd and main switch terminal clamps.

rcds/mcbs are mem old 3871/4293 type, dunno about house end ive not been able to get access in there yet but assuming they are of similiar age

also not sure of tx location
 
This reads plain to me but a few are not reading the OP properly ...

At mains there is a 3ph board with 100mA rcd main switch
Also a 1 phase supply straight of the meter via a henley block to a sw/f + RCD ...lets assume 100mA

When a fault trips the rcd of the 3ph board the rcd IN THE house trips so assuming a 30mA is tripping in the house possibly 17th edition board.... can the OP confirm this!?


Edit confirmed in post 15.


Spot on darkwood yes 100mA s type sp protecting submain(this is holding fine but the 30ma rcd in house is tripping out with the 3pn board in the barn)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Essex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Rcd head scratcher
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
35

Advert

Thread statistics

Created
Welchyboy1,
Last reply from
Engineer54,
Replies
35
Views
4,410

Advert