I use a short extension lead with the earth looped out so I can clamp it the see what is leaking when I plug in.
Hi,
You DO need an earth leakage tester to fault find this, any appliance with an earth connection may legally leak up to 3.5mA through the mains filters and you will not see this on a megger test. A 30mA rcd must trip between 15mA and 30mA.