Well I split the ring between living space and kitchen, and before disturbing the CU wiring too much decided to identify which phase supplied which ring, so far so good. Then traced round each half of the ring to check resistance between the socket where I split the ring and the others on the each half. joined phase and neutral at the split and measured across phase and neutral at each socket. Obtained nice set of readings between 0.37 and .49 for each socket except 1 which was 0.8 checked the connections in the back this one and found neutral needed tightening, this socket then read 0.38. I then livened up the living space radial , no trip. Disconnected and livened up kitchen radial ,no trip! Reconnected the ring where I had split it and livened up the whole ring, No Trip! Performed Z1 using Fluke and reading was 0.51 ohm and 431 amps. So have not carried out the Ir yet and am awaiting the next trip , if it happens.