Whats a Z1 test ?
Something from Top Gear?
yes....its called `see how fast you can get round the circuit`....
Whats a Z1 test ?
Something from Top Gear?
Whats a Z1 test ?
Something from Top Gear?
aye and if it goes to fault while he `tests` this circuit with CPCs disconnected he could end up pinching one off n all (involunatry)If the OP is using a fluke mft and doing dead tests then he would be setting his tester to "Rlo" for a low ohm continuity test and not Z1 as this is for loop tests.
Im thinking that it could have been a "pinched" Line conductor on one of his steel k/o boxes, and he has just been lucky that when screwing the socket outlets back after testing the orientation of the conductor has been altered and now not causing a L-E fault.
Just as a note to the OP. If you do go back and carry out IR tests, then leave the CPCs in the earth bar when testing!
If the OP is using a fluke mft and doing dead tests then he would be setting his tester to "Rlo" for a low ohm continuity test and not Z1 as this is for loop tests.
Im thinking that it could have been a "pinched" Line conductor on one of his steel k/o boxes, and he has just been lucky that when screwing the socket outlets back after testing the orientation of the conductor has been altered and now not causing a L-E fault.
Just as a note to the OP. If you do go back and carry out IR tests, then leave the CPCs in the earth bar when testing!
imp:can someone translate the above please lol
Just been called out investigate RCD tripping on downstairs ring at my parents it just went in the early hours with no history. Have unplugged all appliances from the 10 sockets on this ring and switched all sockets off. There are no other appliances fed from this ring other than those plugged in via sockets. There are 3 other circuits protected by the same RCD in the CU ie Shower, Cooker and upstairs ring, these are all functioning normally and don't trip the RCD. I have substituted the downstairs ring MCB but the circuit still trips the RCD immediately when the MCB is switched on with nothing plugged into the sockets. My next step is to disconnect the ring, split the dead ring at the midpoint and test each half, but before doing this I removed the 2 CPCs for the ring at the CU from the earth bar and the circuit now stays on and doesn't trip. Before I plough on , disconnect the phase and neutrals and do dead circuit testing is there anyway that I can identify why the disconnection of the CPCs allows the ring to operate? Graham
Very Good point esp if carrying out an Ir on a full installation. If you've narrowed the problem down to one ring and need to check Ir on wiring between sockets , would it still be best to leave the cpcs connected I the sockets and just remove the conductors between the suspect sockets to Ir check LE and LN leakages?Sorry got to be quick, but if you removed cpc,s from met, tested IR, then how would you know if there was a fault from a live conductor to any extraneous metal in that installation?
Therefore by keeping the cpc's in the met and putting your test lead on that and your other lead on the circuits L or N, then you will be verifying that all earth parallel paths are isolated from live conductors.