"Didn't have time to IR test as customer was going out"!!!!!
Mate that's the first thing you should have done. Farting about ramp testing and unplugging things, waste of time. Leave everything plugged in and do a 250v test LN-E. Five minutes will establish whether a fault is present. Only when you know what you are dealing with can you make an informed decision on how to proceed, then its time to start farting about unplugging things.
Sorry but it always leaves me open mouthed the number of electricians who come on here about tripping RCD's and haven't carried out IR tests.
 
"Didn't have time to IR test as customer was going out"!!!!!
Mate that's the first thing you should have done. Farting about ramp testing and unplugging things, waste of time. Leave everything plugged in and do a 250v test LN-E. Five minutes will establish whether a fault is present. Only when you know what you are dealing with can you make an informed decision on how to proceed, then its time to start farting about unplugging things.
Sorry but it always leaves me open mouthed the number of electricians who come on here about tripping RCD's and haven't carried out IR tests.

...You're gonna upset lad's who charge by the hour,with advice like that...;)
 
Thanks lads. I was hoping somebody would tell me it wasn't a N-E fault though ;) the house is rank and really don't want to spend any length of time in their!
bloody defeatist. ( and it's there, not their).
 
thanks, pete. that's my 1st agree since the last 1. :D:D:D.
 