AJT83
Hi,
Recently got called to a job, a problem with the RCD tripping. Went through the usual procedures of unplugging everything however I realised it wasn't just tripping on one circuit. It trips if you turn the shower on, plug something into the cooker switch and if you plug something into the ring main. Did a ramp test on the RCD and got 27ma. Didn't have time to IR test as the customer was going out. Was hoping somebody could point me in the right direction for when I go back. I presume it's a Neutral - Earth fault but I just don't understand why it trips on 3 different circuits? Even just trying to get a ZS at a socket or the cooker switch trips it (obviously on no trip).
Customer did say they had a leak not so long ago though but don't see why that would cause a fault like this. The RCD just wouldn't reset if that was the case?
Thanks in advance
It's a split board. Non rcd with just lights which are fine and an rcd side with shower, cooker and ring main. All breakers stay on and the rcd is fine running his boiler, tv, PlayStation etc but if I turn the shower on it trips, if I plug anything into the cooker socket it trips and likewise with the house sockets. If I try and get a ZS anywhere it trips!
It's worked fine for years apparently and not had any electrical work done recently.
If it is that the RCD is tripping when circuits are drawing a high current, then that indicates the fault as described quicker by Telectrix :(.
There would be very little pd for current to flow down a (relatively) high resistance fault in stead of just down the very low resistance neutral and only a small proportion will make it through, but if the small proportion exceeds 30mA because the total load is high then the RCD trips.
You could suddenly twist your ankle/sprain wrist or similar and ring them to say sadly you can't get there for 4 weeks or so.... Not that I condone such things of course. :)
"Didn't have time to IR test as customer was going out"!!!!!
Mate that's the first thing you should have done. Farting about ramp testing and unplugging things, waste of time. Leave everything plugged in and do a 250v test LN-E. Five minutes will establish whether a fault is present. Only when you know what you are dealing with can you make an informed decision on how to proceed, then its time to start farting about unplugging things.
Sorry but it always leaves me open mouthed the number of electricians who come on here about tripping RCD's and haven't carried out IR tests.
...You're gonna upset lad's who charge by the hour,with advice like that...;)
Reply to RCD TRIPPING - ADVICE PLEASE in the UK Electrical Forum area at ElectriciansForums.net
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...