Hi,

Recently got called to a job, a problem with the RCD tripping. Went through the usual procedures of unplugging everything however I realised it wasn't just tripping on one circuit. It trips if you turn the shower on, plug something into the cooker switch and if you plug something into the ring main. Did a ramp test on the RCD and got 27ma. Didn't have time to IR test as the customer was going out. Was hoping somebody could point me in the right direction for when I go back. I presume it's a Neutral - Earth fault but I just don't understand why it trips on 3 different circuits? Even just trying to get a ZS at a socket or the cooker switch trips it (obviously on no trip).

Customer did say they had a leak not so long ago though but don't see why that would cause a fault like this. The RCD just wouldn't reset if that was the case?

Thanks in advance
 
It's a split board. Non rcd with just lights which are fine and an rcd side with shower, cooker and ring main. All breakers stay on and the rcd is fine running his boiler, tv, PlayStation etc but if I turn the shower on it trips, if I plug anything into the cooker socket it trips and likewise with the house sockets. If I try and get a ZS anywhere it trips!

It's worked fine for years apparently and not had any electrical work done recently.
 
If it is that the RCD is tripping when circuits are drawing a high current, then that indicates the fault as described quicker by Telectrix :(.
There would be very little pd for current to flow down a (relatively) high resistance fault in stead of just down the very low resistance neutral and only a small proportion will make it through, but if the small proportion exceeds 30mA because the total load is high then the RCD trips.
 
You could suddenly twist your ankle/sprain wrist or similar and ring them to say sadly you can't get there for 4 weeks or so.... Not that I condone such things of course. :)
 