Can I suggest that you post as many pictures as you can. of the DB, breakers/RCDs/equipment/tags on the gear etc etc........
 
It sounds like it tripping on inrush then, a C type may cure this ( no promises) but is only an option if the ELI would comply to regs otherwise plug into a Ring main elsewhere and i suspect you wont have any problems as this other Ring should have a 32a mcb covering it which is the problem with the shed as you cant upgrade the mcb to larger size due to supply cable size.
 
Plug into a standard ring main i believe this will cure your problems ...the shed set-up dosn't sound like you can adapt it to work and yes the motor inrush on the 16b mcb sounds like your culprit.
 
So if I don't find a problem at the workplace tomorrow then I could upgrade to 32a and place cable with 6mm?
 
So if I don't find a problem at the workplace tomorrow then I could upgrade to 32a and place cable with 6mm?
You mentioned you supply to shed is 2.5 if im right this means you cant upgrade this mcb without upgrading the shed supply and i wont make suggestions because it really needs to be looked into on site .. a little bit of missed info' could end up with you getting incorrect advice.
Its clear (no disrespect meant) that your not an Electrician as you struggle to identify the protection devices so i advice you get someone to have a look what it would entail to increase the mcb rating to the circuit as it may require a new shed supply etc etc..
 
Well, I took the saw in to work today and tried it...... Ran sweet as a nut!!

So, it looks like I need to upgrade my supply. I had a word with one of the electrical guys at the calibration site this afternoon and he reckons change from B16 to a C20. I since checked the supply and discovered that it is actually 2.5 SWA cable on a run of approx 8 meters not twin & earth like originally thought.
 
How is the shed/garage fed from the house? Does it have its own breaker or is it fed from the sockets via a spur or something. You may end up passing the problem further up the chain as it were. C20 is worth a try, there is the little issue of having a good enough earth to make sure it trips when required if there is a fault. Could one of you electricians at work do a drive by and measure the Zs from a socket in the shed, will only take a minute, then at least you and your shed are safe.
 
Obviously a "drive by" doesnt mean the same in your area as mine,if it did he wouldn't need to worry about his electrics afterwards lol:66:
 
It's straight in to the board on its own breaker, so I'm guessing that there shouldn't be a problem
 