M

markthespark

Hello all, while i was away, the RCD kept tripping intermitantly at the house which my mum rents out, so the letting agent got their electrician to go round and he couldnt find the fault so he changed the RCD for a main switch as a temp measure.

When i got back i went round and installed 2 waterproof boxes on 2 cables that were outside that could have been exposed to water and i also changed the main switch back to the RCD. Turned it on and it was fine so i thought it was job done.

This was around a week ago, just recieved a phone call this morning to say it has tripped again, so i told her to turn all the breakers off and turn them on 1 by 1 to locate the circuit where the fault is. However its tripping the RCD when both 6A Lighting MCB is switched on and also 32A ring main MCB is switched on. She also mentioned that it tripped when her son tried to use the Electric shower, which is on a separate 32A breaker.

Anyone got any idea what it could be?

Im thinking faulty RCD maybe?

Many thanks.
 
could be numerious things - great things RCD's but can be a complete pain in the but when things like this happen.

First thing to check for would be earth leakage - try putting a clamp meter on the to measure the current flow on the Line, Neutral & Incoming earth to see if there is (or how much) leakage there is to earth. - probably have to change back to main switch while doing the tests.

Next start insulation resistance tests on each of the circuits - bit of a pain, but sometimes the hard way is the quickest - dont forget to disconnect everything from the cct on test.

Had one of these last year in an old rambling property - took ages to locate the problem.

Best of luck.
 
Thank you very much for the replies.

A neutral fault did cross my mind but if it was a neutral fault wouldnt it trip the RCD regardless whether the MCBs were turned on or off.

The RCD is holding when the lighting and sockets MCB is switched off. So usually id think it was a L to E fault. But as its tripping on both CIrcuits im not so sure.
 
FIREWALSHY

if you post a rough location of the property, a reliable electrician may well offer to have a look for you.

You need a sparky to ascertain what is wrong, everything so far is a guess! No point randomly changing things!

The RCD could be faulty.It'll take 10 minutes to find out (thats with a cup of tea). but to do it you need a spark with a calibrated meter!
 
As you know a rcd needs a level of leakage current to operate,a neutral earth fault on the system can operate the rcd when that level of leakage is reached

If the neutrals are linked via the consumer unit,the load current for any circuit on that rcd is able to operate the rcd with current flow via the common neutral-earth fault,

You may then get the symptom of various circuits tripping the rcd until they have the neutral earth circuit disconnected to remove the common connection

Test as others described
 
If it is a neutral fault, im wondering why it only trips when 2 out of the 8 MCBs are switched on. Never had one like this before, usually it is pinpointed to 1 circuit, cant work out y more than 1 circuit is involved.

BTW im away again so im not at the house to the investigate, iv got my electrician mate there.

Cheers.
 
Yeah i have advised my Electrician mate to disconnect each neutral and hopefully he will find it that way.

If not, when i get back i will IR all the circuits and teat the RCD.

Much apprciated.
 
If it is a neutral fault, im wondering why it only trips when 2 out of the 8 MCBs are switched on. Never had one like this before, usually it is pinpointed to 1 circuit, cant work out y more than 1 circuit is involved.

BTW im away again so im not at the house to the investigate, iv got my electrician mate there.

Cheers.


Well my own and others posts was a waste of time
last tip, Applied Load
Bye
icon10.png
 
Definitely not mate ha, i really appreciate everyones comments, always helps to have a 2nd, 3rd or 4th opinion on it.

Looks like its a neutral fault on the lighting circuit, when its disconnected, all circuits hold.
 
Good point actually mate, but iv lived in this house since it was new, until my mum decided to rent it out so im pretty sure theres no shared neutral.

Thanks for the reply.
 
Let us know what the crux, the nub, the nibbet of the problem is when found. And a picture!

Like this one - a classic N-E fault that presented as IR of 0.0 Meg Ohms at the CU, on the lighting circuit.

Can you see what the problem was?

ebac2650 105.jpg
 