Been looking at what type RCD should be fitted for small single phase individual UPS.
Looked at Hager rcd selection guide under type B has 3 phase UPS but nothing for single phase .


I am hoping type A will do ?

Happy New year in advance !
 
Can the UPS manufacturer confirm that any DC leakage from their unit will be limited to less than 6mA for the duration of its serviceable life?

Why do you feel that Hager not specifically mentioning single phase UPS in their selection "guide" is sufficient to determine type of RCD required - especially given the fact that their 3ph selection guide suggests that type B protection is required?
 
Are the UPS on normal socket supplies and for non-skilled users? If so some RCD protection of the sockets is needed, the question then is if it need be type B RCD or the (easier and cheaper) type A.

Bear in mind that the RCD on the supply to the UPS will not protect against shock on the outputs as when the RCD trips the UPS will merrily keep powering the load and/or poor sod attached to that!

If you are looking at data centre style of operations (and a TN supply) then hard-wired UPS, or risk assessment and area only used by skilled or instructed (electrically speaking), and no buried cables < 50mm from surface, it would mean it makes no sense for RCD protection on the UPS inputs and if supplying areas folks could touch then RCD on the output might make more sense.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Fareham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Roy Bailey

Thread Information

Title
RCD type- A or B to supply single phase UPS
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
Green & Yellow,
Last reply from
pc1966,
Replies
3
Views
2,428

Advert

Back
Top