If the earthing system is TT then obviously depending on the Ra, the cable will need RCD protection of say 100mA S type to cover earth fault protection and also to avoid any nuisance tripping/discrimination issues.
If a TN system then no as the Ze 'should' be low enough for the fuse/MCB to offer the earth fault protection.