I have a SWA cable running from my cu in the house to a cu unit in the garage. Does this cable have to be RCD protected?
 
If the earthing system is TT then obviously depending on the Ra, the cable will need RCD protection of say 100mA S type to cover earth fault protection and also to avoid any nuisance tripping/discrimination issues.

If a TN system then no as the Ze 'should' be low enough for the fuse/MCB to offer the earth fault protection.
 