evening all

I am wondering what the installation methods should be for cables run under floor boards and then into stud walls but without thermal insulation...102,103 dont seem relevant and so my understanding leads me to think it would be a cross between c for clipped direct under the boards and then b for in the stud wall as its similar in a sense to a void.

Thanks for any responses
 
Sometimes you have a mix of installation methods for a cable, and picking one method is not strictly accurate - I would just pick the worst applicable.

For cables under floor boards with no insulation, if this is above a plasterboard ceiling then I'd just put method 100 - which says less than 100mm insulation - which is still true, since there is no insulation. If under ground floor floorboards, then hopefully the cable is clipped to joists i.e. C.
 
Go with worst choice, most cables I find under floorboards on ground floor down here are just lying on the cold earth.....no install method for mud though ?
 

Reply to Reference methods for cables ran under floorboards and into stud walls no thermal insulation in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hi All I wanted to ask a question about the reference method. Passing wiring through holes made at 0.2-0.4 of the joist span. The cables passes...
Replies
1
Views
1K
Hello guys, I‘ll be building an insulated stud wall in front of a single skin brick wall (garage on the other side). There will be 2 couple mains...
Replies
0
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
655
I am wondering what the installation methods should be for cables run under floor boards and then into stud walls but without thermal...
Replies
3
Views
994
hello theres a damaged cable under floor boards in either the living room, hallway or dining room. the 'downstairs sockets' mcb type b in...
Replies
41
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock