Just your thoughts on this one,doing a part refurb on existing offices,no initial verification or certs found anywhere.
Premises rewired bout 1990,adding sockets here & there in each room.
The DB is a Crabtree Tpn polestar,just finished some loop readings ,& not good,1.49 the highest,there is no rcd protection on any of the circuits,the ring mains are of a 3871 type 2 32 amp.
We are now waiting from architect or whoever on what to do.
In the meantime bit concerned about our new additions,should I refuse to connect them up.