Discuss Replacement board TNS supply and TT in the UK Electrical Forum area at ElectriciansForums.net

J

Jimmyb

Hello, just after people thoughts, I have been asked to replace a consumer unit (original is plastic) and the cable feeding the house is supplied from a switched fuse 60meters away with no rcd protection, the first 18meters is 16mm twin and earth and the rest is 16mm 4 core with the 2 cores doubled up and the steel used as cpc. (the house has barely any load as has oil boiler, arger cooker and no showers ect)
They had someone else a few years ago pick up on the fact that the earth is undersized so he installed a rod and made the house TT. all good and well at the time.
Now I want to/have to install a metal board and was wondering which is the correct way to go about it

1. Gland the swa into a separate enclosure before the consumer unit and run the core of the swa though conduit and into the cu. (zs too high for switched fuse so a no go)

2. Gland swa straight into consumer unit (cant do due to undersized cpc so again a no go)

3. Add 100ma T/D RCD enclosure before consumer unit then conduit into consumer

I don't really like the sounds of option 3 due to the cost of a T/D rcd but I cant think of another way


Many thanks

Jimmy
 
Hello, just after people thoughts, I have been asked to replace a consumer unit (original is plastic) and the cable feeding the house is supplied from a switched fuse 60meters away with no rcd protection, the first 18meters is 16mm twin and earth and the rest is 16mm 4 core with the 2 cores doubled up and the steel used as cpc. (the house has barely any load as has oil boiler, arger cooker and no showers ect)
They had someone else a few years ago pick up on the fact that the earth is undersized so he installed a rod and made the house TT. all good and well at the time.
Now I want to/have to install a metal board and was wondering which is the correct way to go about it

1. Gland the swa into a separate enclosure before the consumer unit and run the core of the swa though conduit and into the cu. (zs too high for switched fuse so a no go)

2. Gland swa straight into consumer unit (cant do due to undersized cpc so again a no go)

3. Add 100ma T/D RCD enclosure before consumer unit then conduit into consumer

I don't really like the sounds of option 3 due to the cost of a T/D rcd but I cant think of another way


Many thanks

Jimmy

I am most probably reading this wrong, but are you saying that the electric meter for the house is 60 meters away from the house and the cable between the meter (ok the switched fuse next to the meter) and the CU is "16mm twin and earth and the rest is 16mm 4 core with the 2 cores doubled up and the steel used as cpc"
 
sorry if I written it bad, it start at service head, 25mm tails into the meter then 16mm tails into switch fuse, from there it 18meters of 16mm twin and earth upto a joint box and then it swa cable for the out side run into the house
its a farm which has 4 house all feed from this area, they said it all was twin and earth but had to replace it where it was outside due to damage and they thought it best to put a bigger cable in, I did ask why not all the way back to the switched fuse
 
63c6dbe8070f0bba9c21495febec0578.png
You could use an insulated gland.
 
sorry it prob will be 6mm, I'm not 100% of the size that the steel works out to be and also there is bonding to take in account so when I thought it was 4mm I didn't think its up the job and neither did the last man.

it actually works out at 3.21mm so might be ok, I just wonder why the last guy has tt the install
 
Last edited by a moderator:

Reply to Replacement board TNS supply and TT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
863
I have added a consumer unit and an earth stake to this so called temporary supply. This is a full rcbo board apart from the mcb to the spd...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock