Discuss Requirements for a small kitchen in non domestic situation. in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
I have been asked to wire up a small kitchen for a local charity.

1 x 32a cooker
4 x sockets
fridge/Dishwasher
Cooker Hood
2kW water heater

It's a drop in centre, not a commercial kitchen.

It's a little out of my comfort zone with regards regulations though.

At present it is just a storage area, it has a fire alarm in it which looks similar to the one in the picture below. I expect it will be optical.
fire alarm.jpg

My questions are..

1. Do I need to use LSZH cable for all new cables?
The kitchen will not be an escape route.

2. Can I change the fire alarm for a heat alarm?
If this was domestic I would simply change it for a heat alarm and make sure it was linked to the others. Is this the same with this type of alarm? Will it just be a PL, N and link wire?

3. Are there any other requirements/regulations?
This is purely in addition to domestic regulations which I am fully aware of (eg 300mm from sink etc etc.)

4. Is it ok to have cables loose in the ceiling?
In these type of premises I always see the cables loosely sitting above the ceiling. It is those small square removeable tiles in the ceiling interlaced by small metal strips keeping them in place (not sure what this is called). Is it acceptable to have them like this or should there be some kind of containment?
 
Last edited:
Stop worrying hippy and wire it up. No different than house.
Design install test
I noticed one person had replied. Great I thought, all 4 questions will be answered. I suppose in a way they were ?
 
You should just be able to swap the smoke head for a heat if they are still in production, twist off put the new one on and I would complete a fire alarm modification certificate. Cables in the void must fixed to prevent premature collapse but containment isn't necessary. Location of accessories is no different no matter the type of kitchen, it is really just external influences.
 
The smoke detector looks like a panel job. It won’t be mains powered (12v possibly?)
Should be able to just twist it off it’s base and replace with a heat, but ask the building supervisor in case doing so sets off the alarms.
 
The smoke detector looks like a panel job. It won’t be mains powered (12v possibly?)
Should be able to just twist it off it’s base and replace with a heat, but ask the building supervisor in case doing so sets off the alarms.
It won't trigger an alarm but should indicate a fault at the control panel.
 
If you're altering the design of a fire alarm system to BS5839-1, you should really know what you're doing and as Westward10 says, issue an appropriate certificate.
Otherwise, find out who is responsible for the maintenance of the fire alarm and get them to change the head and issue a certificate. And write it in the log book.
 
That looks Apollo/Alarmsense, which is a quirky 2 wire system.
I'd agree that the fire alarm will (should) already be maintained by someone- make that bit their problem. It's a simple job for them.
EDIT starting to wonder if it's XP95 addressable - definitely don't touch!
 
Last edited:

Reply to Requirements for a small kitchen in non domestic situation. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
917
I know this has been brought up before but as a QS for a housing association ,i have been asked my opinion on interpretation of the regulations...
Replies
11
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock