bigdavs83

Had some rcbo's to retrofit to some dorman smith 3 phase db's earlier and it occurred to me as I was fighting past the other cables in the 72 way board that they are actually a nightmare to fit in a busy as heck board. Why they so bloody long?!?!
 
The long nose pliers were a godsend today!! It would make a difference if the previous sparks had tidied as they went along plus all the neutral flying leads were like a dogs dinner
 
I think it might contain a "flash chamber", as a firm (ECD) did peddle some RCBOs the same size as an MCB for a bit and the "flash chamber" was omitted to make them small. I seem to remember.

but seeing as all other RCBOs are that size, maybe it was a bad idea....


there yerz go....

Compact RCBO Mini RCBO Circuit Breakers

koolashaka.
 
I think it might contain a "flash chamber", as a firm (ECD) did peddle some RCBOs the same size as an MCB for a bit and the "flash chamber" was omitted to make them small. I seem to remember.

but seeing as all other RCBOs are that size, maybe it was a bad idea....


there yerz go....

Compact RCBO Mini RCBO Circuit Breakers

koolashaka.


Still very much available by all the major manufacturers like ABB, MG etc, and used extensively in Europe. They are 1PH + N rather than true double pole....
 
Think the problem with these rcbo's is they don't normal fit onto a buss bar very well, so not very good for retro fitting into an existing mains, i've used them in the leisure side of electrics where you wire them up using panel wire so there are ok
 
Think the problem with these rcbo's is they don't normal fit onto a buss bar very well, so not very good for retro fitting into an existing mains, i've used them in the leisure side of electrics where you wire them up using panel wire so there are ok


They would normally be fitted to a CU/DB with a DP (N-E) busbar, similar to what you would see on a 3 phase DB... Modern French and German domestic DB's, have such single phase arrangements as they make use of DP/1PH-N protective devices quite extensively...
 

Reply to retro fit rcbo's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just thoughts Id share my recent fun and games on my parents farm.. The electrics are old. Its a 400yr old house with outbuildings just as old...
Replies
9
Views
1K
Hi everybody. In the not too distant future I would like to get my current consumer unit replaced. I want to select the brand for my electrician...
Replies
43
Views
20K
I have an Install where a 16mm 4core has been installed previously. ATM the SWA is coiled up either end At the supply which is a barn converted in...
Replies
12
Views
2K
B
I have been testing an installation with lot of RCBOs recently and found that a significant proportion of them will pass at 30mA fail at 5X30mA...
Replies
9
Views
6K
BlueToBits
B

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock