just want to tell you about a fault i had to fix yesterday.
I was doing a periodic report and when i did the ring final test it showed
a line to earth fault. Old wylex board no rcd. After a few hours of breaking the ring down i found that a screw was touching the line conductor only in a concrete wall. So you might ask how then can there be a line earth fault.

What i discovered was the wall was damp and so the dampness was acting as a conductor carrying current to the nearest earthed metal
socket box in the concrete wall thus giving the earth line fault.

Im quite new to this game and was chuffed to find the fault:d​
 
i had one like that well nearly ,used to work in castles doing the maintainance ,cables were embeded in the joints of the rock covered in cement ,not right realy but with the restrictions of what you could do to install the cables ,very wet and dark lights , one day they lost the lights would stay on for 10 mins then trip the breaker , imagin a castle big walking along the passage ways found the whole wall was live ,hair standing up not because of the haunting past ,lol , could here a slight crackling withing the wall ,yep the cable had burnt out behind the cement and was arching ,so i know how you feel finding a fault like that ,nice one:)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
ring circuit line earth fault
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
m25maintenance,
Last reply from
nickblake,
Replies
3
Views
2,585

Advert

Back
Top