- Reaction score
- 38
A 100mA RCD fitted up stream of a 30mA RCD might still trip for before the 30mA, it depends on the individual components. The only way to RCD cascade a distribution circuit is to use a 100mA time delayed RCD, which will not count as additional protection (415), nor would a normal 100mA for that matter