Discuss Satisfactory or Unsatisfactory in the UK Electrical Forum area at ElectriciansForums.net
I
Industspark
Hi fella's ,
Following a recent report I have had sent to me t was deemed that multi-core SWA doubled up to
supply a single phase piece of equipment, was unsatisfactory for following reasons.
'Poor onsite installation practice may result in increased risk of failure,electric shock or fire'.
See photo.
To me I understand that it is bad practice to not correct size cable on the original install, however what regulation does it no comply with and is it really a C2?
I mean we do it for larger install supplies.
I can only imagine that this is the only cable they had at the time of installation and they've used 2 cores the Live, neutral & earth.
they marked it as C2 because they deem unsafe. It's bad practice but is it unsafe for continued use?
more detail needed. is it 2 cores for L and 2 cores for N? as in parallel conductors? the cpc may or may not be adequate if it's a single conductor, esp if there's extraneous parts that require bonding.
Looks like there are 2 separate circuits within the same multicore cable. Second and fifth (from top) MCBs seem to be using cores within this same cable as line conductors.
Indeed....two circuits,a radial and RFC? Only got the BRB to hand at home,the reg number may be different in the BYB....but 521.7 applies, two or more circuits are permitted in the same cable provided the usual requirements are met in section 528. No code needed as far as I can see.
Yep I'm aware of that reg. I didn't say anything was technically wrong with it, was just trying to determine what the report could have been alluding to. The report statement is so vague it's hard to tell. I couldn't see it was from the doubling of the conductors.
Yes...I spotted that it was two separate circuits and not one as stated in the OP....and never thought you were stating that there was anything wrong with the installation method. In fact it looks like a pretty neat job!
Only a problem (and obviously not in this case) if the circuits are for VFDs, the 3 cores must be symmetrical to comply with the EMC regulations. So no multi ores like that.
A bit off topic but a useful nugget of info.
I was under the impression you were allowed to double up cables. I may be able to get you a reg number tomorrow if anyone needs one?
Reply to Satisfactory or Unsatisfactory in the UK Electrical Forum area at ElectriciansForums.net
Background: I have a ex council 1st floor flat that I bought, I moved in to care for my disabled mum and so rented the flat as I could not do...
5K
Am currently pondering the following situation: - Single phase PVC board, domestic, in an area where TN-C-S is the norm (underground supply etc)...
Self Employed Electrician Insurance trying to start off, As you know my English isnt that great so LAWER talk and Insurance sadly i was in the...
DuaneMHunt1976
Please take some time to read through this. It is written by Widdler's father. I found it on a governement website.. It certainly speaks my mind...
C
Many thanks for the numerous thoughtful responses to my initial post. I think the threads have become too long for members to spend time...
9K
sparkinlee
S