Discuss Secondary Transformer Circuit Breaker in the Industrial Electricians' Talk area at ElectriciansForums.net
Hi, I'm just curious about what will happen if I use an MCB lower than the calculated current rating. I have a 1kVA 220v stepdown to 110V transformer, calculated downstream MCB current rating would be 11.3625 if i'm right I multiplied the secondary current to 125%? what will happen if I use a lower MCB current rating?
MJ what size breaker do you have the primary is going to pull 4 amps and the secondary will pull 8.3 amps
I'm planning to put 6amps on primary whilst on secondary i'll put 10amps? I was thinking that the proper breaker size for the secondary would be 1000/115 = 8.69 x 1.25 = 10.69amps?
MJB where are you getting the 125% from. That transformer is not going to withstand 10 amps. Divide 1000 by 110vac on the secondary and see what that transformer will withstand, it should be on the nameplate.
You don’t “put” the current on the primary. The amount of current that flows through the primary winding will be proportional to the current being drawn by the load in the secondary.
Th
Tayler it is a 1000 watt transformer it is not going to withstand 10 amps, it will start running hot. I did the math for yall
[automerge]1567614974[/automerge]
Th
Th
Taylor no joke do you agree with him
I measured the output voltage of the secondary and it's 125V, calculating the current 1000/125 = 8Amps, by putting an MCB higher than 8amps, it would make the transformer hot right and burned eventually? To protect the transformer you would rather chose an MCB that's lower than 8amps? You're bloody spot on mate! Cheers on that!
All of this is irreverent if the OP want's to use the transformer for a fixed piece of equipment. It may only need 2A.
What is it you are wanting to use it for?
Fit an 8A breaker you'll be fine.
A 10A 24V power supply doesn't need more than 240 watts on the input side, so at 120V 2 amps maximum. PLC will likely require 1 amp maximum. An unless you've dozens of contactors using the 110V and not the 24v then this will be less than 2 amp of load.
Reply to Secondary Transformer Circuit Breaker in the Industrial Electricians' Talk area at ElectriciansForums.net
Hi everyone, I need help installing a Lorex smart doorbell. I have tried to install a doorbell transformer several times to no avail. The first...
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...