Thanks @baldelectrician thats why I am asking the questions.

If I forget that I have PV at the moment, and go with a grid charged battery… get an electricity tariff with lower night time and charge overnight, use during the day… it won’t matter if I get a 3, 5 or 10 kW (or whatever) inverter for the battery…. And I can locate it wherever…. I just think the attic is not a good place.

Making use of it by changing what I can to electric… hob, for example… but there’s nothing much can be done with the gas combi boiler with no tank.


Thinking of the PV now, will the battery side know when the sun is shining and let the PV take the load, or would the two invertors need to talk to each other somehow?
Likewise, will the battery’s charge off the PV (after the FIT meter) before charging from grid?
 
With the Giveenergy the PV is wired directly to the All in One hub, this means the PV is also powered when there is a power cut (direct from the battery storage) and it also will know what you are importing and exporting.
You can also set priorities for each thing, the best option is to generate the PV (the meter on the PV system will register this) and store the energy

Just to note- DO NOT get a smart meter as they can switch you from deemed export (via solar meter) to actual export (registered from the smart meter), you will lose money with a smart meter if they decide to use actual export
 
i have no desire for a smart meter just now.... Not because of the conspiracy thoughts that they can cut you off/ change your tariff/ spy on you etc.... but more because i do not think the technology is quite there yet...

I mean, i have a simple energy monitor CT around the tails, but it doesnt know the difference between grid load or PV going back.


However... if i need to change tariff or supplier to mske use of overnight cheap rate... will i be forced to take a smart meter?
 
Up in the north SiS meter people told me last week that they have less than 18 months of non smart meters left. After that people won’t get a choice - it will be a smart meter or nothing.

You can have a second PV system and a battery. We did. Puredrive system with 3 PV systems and 3 inverters. 2 are on a FIT. Clamp on tails and the. Another on the chosen PV system. The other 2 are not affected.
 
Late to this one but have a look at teh givenergy All in One with 13.5kwh of storage 100% depth of discharge. it can be installed as ac coupled on its own to utilise solar/ac charigng, if you wanted then now or later you can add the gateway for full house back up. only costs £350 for the gateway seperate. the full AIO is around 4.5k depending where you shop.
 
I’ve gone with the offer, but only took the battery and inverter, none of the sundry items.

It got delivered to the house yesterday, and the battery box is H E A V Y

No idea how I’m going to get it into the attic.


I’ve not gone high… it’s a 3.6kW inverter, and a 5kwh battery… but as I’m paying, it’s more of a practice job.
Any paying customer, I’d push for higher.


All the instructions are online. And I’ve already got spare parts I don’t need.
There’s a usb type device with 2 screw connections that came with the battery, but I can’t find reference for it in the manuals.


I’ll have to see how to split my PV into 2 strings. I’ve definitely only got one, as there’s only 2 wires going into my existing inverter.

2 rows of 8 panels… so I’ll just have to split the rows.
 
LiFePO4 chemistry is considered to be relatively safe, but I wouldn't place a bank of them in the roofspace of my house.

 
I’m starting to think about extending the DC of the PV down the outside of the house and into the garage. (Vertically directly below the existing inverter.)

Might need to move my beer fridge or freezer…. Or a couple dozen Lego models… to fit it in… but it might be easier and safer.

Might even try on the outside wall… it doesn’t stick out as much as I thought it might. Just don’t want to knock it with the wheely bin.
 
The chances of any issue is probably very low, but the potential consequences of those unlikely issues could be severe. If the garage is at all possible it's where I'd be looking to locate storage. Outside would be better again, but I'm not sure how that might work out in the long term with our climate.
 
I may be wrong but I'm sure Efix did a news cast or similar a few months ago saying latest guidance on battery storage was not to install in a loft!?
yes... ive heard from other installers about that... but theres nothing in MI i can find.

Id be putting in a smoke detector up there eventually anyway.

The Sunsynk invertor comes with a temperature sensor that just sits on the battery box... so will shut down if it overheats... andi was told in CEF that the ICS batterys... (not the ones ive gone for) have a self extinguishing feature.


Im going to measure the space in the garage and outside for suitability.... but theres still the extending of the DC cables from the PV....
Unless i make the battery and new invertor seperate to the PV invertor?? Leave the PV as is, and just charge the batterys from the AC going into the CU from the PV

There should be a way to control when to charge... just when the PV is generating.
Theres a CT clamp for measuring grid consumption.... so that could just be placed elsewhere?


More reading!
 
Not Efix but I did find this and it would seem that you can still fit them in lofts with certain safety precautions taken, as you say @littlespark a smoke detector is a must.

Personally, I would fit the separate inverter and battery in the garage or just outside if there is space and keep them as independent systems only connected through the mains, yes you will loose a bit due to inefficiency but at least if one side fails the other side will still be usable.
The unit will no doubt be configurable to do as you wish as you say more reading to be done on that one!
 
The problem I see is that the amount of energy stored renders regular smoke detection redundant, should the worst happen. Even very early smoke detection systems would be of little use should that amount of energy be released in short order. Not only would the fire service have no chance of arriving in time to do anything, there's pretty much nothing they could do. With EV fires they can only sit back and watch, while trying to protect adjacent property.
 
I have installed my own battery solution based on a Victron (Very high quality) Inverter/Charger (5kVA) and LifePo4 cells. The cells are super cheap right now... you need a BMS to manage them, but it's all super easy to install and setup. Total cost for a system with 12kWh (usable) and 5kWh inverter/charger is about £2.5k... It means that my electricity cost is about 9.5p/kWh on average !

Happy to provide more details if you want...
 