Search for tools and product advice,
Discuss Sense alarm Fire alarm in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net
cliffed
Supporter
having probs with Fire alarm.Its a sense alarm 2 wire,mcp's,detectors & sounders.
Goes into Fire mode,even when only 3 points are on circuit.
Are all their sounders compatible with the system,it's difficult to understand properly ,we have sounders,which are alarm sense,not the sounder & base ones,on their diagram.
Commissioning guy,going round in circles.
Have you connected the bases in parallel (if using standard bases)? Both in and out should be connected to L1 in +ve and L2-ve. Not how you would connect a coventional base using in and out.
As Lee said, break the circuit down & bridge each head or call point one at a time.
I normally keep a set of short jump leads in my kit to quickly bridge things out.
Are you using sounder bases or have a sounder circuit? All the gear is alarmsense? EOL capacitor for detector circuits and EOL resistor for sounder circuits? If using separate sounders are they polarised?
No sounder circuit,all on same circuit,sounders are not base sounders,all alarm sense equipment.They are not polarity sensitive
In the CFP alarm sense manual, the circuit showing the alarm sense sounders shows + - at the sounders.
I just took this to indicate the sounders were polarity conscious, although it doesn't actually say this. Says to look at the manuals for each device.
Just looked on the C-tec website, your right they're not polarity conscious. In answer to your earlier question, it looks like all 5500 series sounders are compatible.
Are you using Apollo Alarm Sense or are you using a 2 wire system.
If your using a 2 wire system then the sounders must be wired reverse polarity. All fire alarms weather on sounder circuits or combined zone circuit, change polarity when in alarm status, this is why bells etc have blocking diodes. Can you state the panel and exact equipment your using
do they have to be wired in reverse? I was reading this link which said they are operated on voltage. Apollo Fire - 55000-017APO - AlarmSense Open-Area Sounder Visual Indicator - https://www.apollo-fire.co.uk/products/range/alarmsense/sounder-visual-indicators/55000-017apo-alarmsense-open-area-sounder-visual
From the first quote its states sense alarm 2 wire systems, this could be Fire Sense, 2 wire system...it could be Apollo Alarmsense, Could be Haes 2 wire....so once we get all the info we can go from there
Sorry about the waiting,all ok now,it was a loose smoke detector,not fitting to base properly.
Always the same the worst one to get at,needed scaffold to reach it.
Thanks for all your help.
Reply to Sense alarm Fire alarm in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net
Hi all, i'm just after a definitive answer regarding a fire alarm system in a communal area/stairwell. There are call points, smoke heads &...
Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on...
4K
Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
I'm about to order this wired smoke alarm system as it can network but I just went to see how my existing fire alarms are hooked up and there...
I'm about to start first fixing this fire alarm in the industrial unit we are wiring, at the moment its totally empty and eventually will have a...
