- Reaction score
- 3,818
Did you try using a half sized cpc in the software in parallel with a 4 core swa?I think there is a bit of confusion here, the thing I was trying to highlight was that the software said it was ok to use a 5c cable with an integral earth conductor, but not ok to use a 4c cable with a supplementary earth of the same size.