Discuss Seperate / Integral earth CPC on 400A supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I think there is a bit of confusion here, the thing I was trying to highlight was that the software said it was ok to use a 5c cable with an integral earth conductor, but not ok to use a 4c cable with a supplementary earth of the same size.
Did you try using a half sized cpc in the software in parallel with a 4 core swa?
 
Did you try using a half sized cpc in the software in parallel with a 4 core swa?
Tried full size cpc in parallel with a 4 core SWA and it just would not have it. I think the software was suggesting either one 300mm 5c SWA or 2 x 150mm 5c SWA, but if I tried 4c SWA + supplementary it threw it out on earth loop value.
 
Tried full size cpc in parallel with a 4 core SWA and it just would not have it. I think the software was suggesting either one 300mm 5c SWA or 2 x 150mm 5c SWA, but if I tried 4c SWA + supplementary it threw it out on earth loop value.
Why not just use table 54.7 and use a half size cpc rather than a cpc the same size as the live conductors?
That's if you want to install the supplementary cpc
 
I think there is a bit of confusion here, the thing I was trying to highlight was that the software said it was ok to use a 5c cable with an integral earth conductor, but not ok to use a 4c cable with a supplementary earth of the same size.
I have been thinking about this and and the only thing that comes to mind is the programme assuming the cpc will pass through a separate hole to the line conductors which would not happen if it were a core of the cable which may under fault conditions be problematic, maybe.
 

Reply to Seperate / Integral earth CPC on 400A supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
603
Hi All, I am currently learning about AC and DC supplied coil and have been given the scenario below. I understand the first few steps but then...
Replies
1
Views
1K
Another long one from me ... I hope that it covers all the bases and is a more thorough approach to the subject. It is my first design work so...
Replies
44
Views
6K
P
A single-phase radial circuit is to be installed to supply a number of socket outlets. The source of supply is 230 V, 50 Hz with a declared value...
Replies
11
Views
2K
F
Here is the second half of the long answer questions. Q 24 a) Describe how an Insulation Resistance test would be carried out on the new lighting...
Replies
5
Views
9K
Deleted member 26818
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock