hi, in part p, it says there is no socket outlet within 3m of a bath, however shaver socket is an exception,why is this, what the main difference of the shaver socket? sorry for this silly question.

cheers
 
In other words segregated extra low voltage. ie it has a transformer that steps down the voltage.
 
Shaver sockets are 230/110 volts and are not SELV, remember Extra Low Voltage is 50V or below . A shaver socket has a double wound isolating transformer. This means the socket is electrically separated from earth, allowing you under single fault conditions to touch a live conductor and earth and not receive a shock. (Because there is no earth path)

crossfig2_l.jpg
 
Last edited by a moderator:
Electrical seperation is the keyword.....roukel's post explains it well. A shaver light/socket contains an isolating transformer in which it's secondary winding is completely isolated from the earth of the supply circuit, thereby eliminating the path to earth for shock current.
 
Last edited by a moderator:
Just out of interest, has anyone ever tried out the theory, and touched the live of an isolating tranny?!
 
Well I have stood on a rubber isolating mat and touched a 240v live conductor (Same principle ie no return path) and I didnt feel a thing not even a tingle. Mind you a sparky I was working with did it first, just to prove his point. All was fine until I shook his hand.:eek::eek::D

Ps, NOT RECOMMENDED.
 
Just out of interest, has anyone ever tried out the theory, and touched the live of an isolating tranny?!

Never touched one, but measured it on a boat's shaver point that was being fed by a 2.5kW modi sine inverter. These have fundamentally diferent characteristics to land-based mains power.

The secondarys of that isolating tranny had a line-earth potential of more than 70VAC!!! Enough to give a tingle for sure.
The line-line potential was 270VAC.

Anybody measured the same on a household shaver point?
 