1stfix2ndfix

I was wondering if anyone can answer this one for me. I'm an electricians mate, I did ask the guy I'm with but he couldn't give me an answer.

So after he changed the board and I did the bonding I get to go round testing. Whilst taking the zs of the shower I noticed immediately upon removing the over that the feed had been wired up wrong. The live was with the live but the neutral from the feed was wired up to the earth terminal/cable in the shower and likewise the earth from the feed was wired up to the neutral terminal and cable of the shower. Now spotting this I asked the customer who had wired this up as they have done it wrong and I was told the fire fitter lol. She then asked me why it had worked and was still working. I didn't really have a answer and nor did the guy I'm with if I'm honest so I'm just wondering if anyone knows the answer to that one. Was it unsafe and were they just lucky. I felt a right idiot not knowing the answer but hopefully next time I'll be able to fill em with confidence in my response
 
A very lucky escape, if the shower had developed a earth fault there is a good chance the pipe work could become live or other class 2 equipment, also any spark working in the DB could have been at risk if they were working in the DB. I take it that there wasn't a RCD or RCBO fitted to the circuit befor the DB change?

The reason it would still work is there is still a return path via the earth cable rather than the neutral.
 
I'm guessing it was the person who fitted there fire lol but I could be wrong. Dillb cheers for the knowledge mate and yes Archie I agree but he didn't seem to so I thought if ask on here and I got a pretty good answer so I'm happy
 
What made it worse was the two screws supposed to hold the cover on at the top were missing and it could be pulled back a good couple of inches. Lucky indeed as it was a rewireable db originally
 
surely if a new board has gone in the shower will be on RCD. when you then switch the shower on , the RCD will trip as current will be flowing L - E , thereby causing a huge imbalance.
 
only way that would have been picked up is by opening the shower and doing a R1+R2 or just a R2. who does that for a board change?
 
That could not have happened as the first thing he does is to cut into the tails and pop a rcd in the middle. If this trips out we know we've got problems. So that is weird either he didn't do it (not likely) or there's something else as the feed coming in was Deffinenty wired up l-l n-e and e-n.
 
That could not have happened as the first thing he does is to cut into the tails and pop a rcd in the middle. If this trips out we know we've got problems.


The plot thickens...

So before he changes the board he sticks an RCD inline with the tails and if this trips you know you have problems?...

ha ha no way!...is there no testing carried out?...(other than the bang test)
 
Testing seems to be cut into the tails and put a rcd in. If it trips then we've got problems if not good to go.

So I'm wondering should the rcd have picked up on this

What tests should of been done and what one would have shown me that the nutral and earth were mixed up in the shower unit before I even looked in there?
 
Testing seems to be cut into the tails and put a rcd in. If it trips then we've got problems if not good to go.

So I'm wondering should the rcd have picked up on this

What tests should of been done and what one would have shown me that the nutral and earth were mixed up in the shower unit before I even looked in there?
no way of finding that fault without opening the shower unit apart from RCD tripping as soon as the shower was used. i've already said that if you read my previous posts.
 
Testing seems to be cut into the tails and put a rcd in. If it trips then we've got problems if not good to go.

So I'm wondering should the rcd have picked up on this

What tests should of been done and what one would have shown me that the nutral and earth were mixed up in the shower unit before I even looked in there?


http://i.stack.Upload the image directly to the thread.com/jiFfM.jpg



I cant believe someone does that. An R1+R2 or R2 would of picked it up, one of the first tests that should of been carried out.

Installing an RCD in line is going to take longer than carrying out that test. As Tel says it doesnt prove much either because it would have to be switched on for it to trip. It is not the right way to do things at all.
 
be honest though, how many of us have opened a shower to get a R1+R2 before doing a board change?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Shower feed wired in wrong
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
47
Unsolved
--

Advert

Thread statistics

Created
1stfix2ndfix,
Last reply from
1stfix2ndfix,
Replies
47
Views
6,227

Advert

Back
Top