Hi all,
Quick question, can you use a 25mm cable from earth bar in C/U to Earth Rod in cellar directly below?
Reason I ask is I need the 3m tails to extend from incoming fuse, and they come with a 25mm earth cable included, so would this be easier than running a new 10mm earth cable to the rod which is accesible in cellar?
I know squeezing in a 25mm cable into the earth bar may be nigh on impossible (depending on C/U), and I'm not wanting to cut strands to make it fit.
Thanks for any advice.