The fuses in the plug tops will stop an overload on the cable. This is no different to tapping of a busbar chamber (industrial) in smaller tails and having a switch fuse inline after a meter or 2 of cable. Protection against over load does not always have to be at the source of the circuit.

So based on this assumption I could wire a single 13A socket on the end of some 1mm cable from a 50A MCB in the CU?
 
To protect our customers, as well as ourselves, we have to comply with BS 7671, the regulations for final socket circuits are there for us all to see. Should we detract from these regulations then we are in dispute with the EAW and in the eyes of the law, we are breaking this Act. If we install socket outlets in line with BS 7671 then, surely we are complying with the current regulations, until someone tells me different, then I will install 13amp socket outlets, in compliance with BS7671, 20amp radials with 2.5mm, 32 amp radials with 4mm and Ring Final circuits 32 amp with 2.5mm
 
Where in the regs does it say you can wire a 2.5mm twin and earth and protect it with a 32 amp mcb you can with an additional fused spur as well as 1.5mm protective device for 2.5mm twin and earth is as stated in the little green book is 20 amp which is an A3 radial ,there is a risk of potential over load , how longs the cable length one bit of insulation will de rate the whole cable I would quite happily put it down as a C2 ,there are so many unfused 3 way adaptors out there i wouldn't risk it

Page 425, Appendix 15 Fig 15A

"An unfused spur may be connected to the origin of the circuit in the distribution board" with regard to connecting one (2.5mm) spur at the CU from the 32A MCB of the ring.

I feel like I'm arguing against the case for doing anything now! I'm not, I dont like it and I'd tell the customer so, but its not breaking the regs.
 
So based on this assumption I could wire a single 13A socket on the end of some 1mm cable from a 50A MCB in the CU?

I think its a good idea to show extremes when getting your point across XT but... you are just looking at overcurrent with the above example not fault current, also it would be completely unrecognised by electricians and therefore far more likely to cause problems and also its against the regs, whereas one 2.5mm spur from the origin would be ok for fault current, fairly recognised and adhere to the regs.

But!! If it was just a 2.5mm coming out of a 32A MCB with no ring then why not advise the housholder to change to a 20A MCB, you dont have to but it seems like a good idea.
 
So based on this assumption I could wire a single 13A socket on the end of some 1mm cable from a 50A MCB in the CU?
No, no, no! Minimum cable size for power circuit is 1.5mm but yes a single 13A socket on a 50A MCB in 1.5mm could be done. (433 & 434 give details of how & why!) Whether you'd want to do it is perhaps another thought ....
 
Reg 434.2.1 could be applied here.

That is a bit contradictory to Fig 15A isn't it!! The only thing I can say to that is reg 433.2.1 doesn't have to be met if Reg 433.2.2 applies, but it doesn't look like it does!

The only other defense I can use is Fig 15A is extremely clear in its acceptance for a spur from the MCB, whereas the reg you have quoted is not as specific.
 
No, no, no! Minimum cable size for power circuit is 1.5mm but yes a single 13A socket on a 50A MCB in 1.5mm could be done. (433 & 434 give details of how & why!) Whether you'd want to do it is perhaps another thought ....

You would not be doing it in my house or any of my jobs, straight out of the door tools first.......!!
 
Appendix 15 is informative and just sets out a possible option for a solution to 433 ...... there are other ways to skin the cat by careful reading and interpretation of the regs!
 

Reply to socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
676
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
926
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
764
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock