Not wired one of these before, it’s an spd type 2 that’s come with board (fuse box)!
Question is does the line from the spd connect in same bus bar connection on main switch???
 
You need to check the data sheet.

Some can go direct on to the main live bus as they only need 160A of fusing as last-resort protection so the DNO cut-out is deemed acceptable, others say to put them on a 32A MCB.
 
You need to check the data sheet.

Some can go direct on to the main live bus as they only need 160A of fusing as last-resort protection so the DNO cut-out is deemed acceptable, others say to put them on a 32A MCB.
You need to check the data sheet.

Some can go direct on to the main live bus as they only need 160A of fusing as last-resort protection so the DNO cut-out is deemed acceptable, others say to put them on a 32A MCB.
You need to check the data sheet.

Some can go direct on to the main live bus as they only need 160A of fusing as last-resort protection so the DNO cut-out is deemed acceptable, others say to put them on a 32A MCB.
thanks for the fast reply?
yep it doesn’t require an mcb.
It came pre wired with its live going in the bus slot! I was just wondering if this was the correct way of doing so?
(Sharing the same slot with the bus)?
Thanks again
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Warrington

Thread Information

Title
Spd connection
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
Garymcdee,
Last reply from
Garymcdee,
Replies
4
Views
1,989

Advert

Back
Top