Hello guys.
I was asked to quote to replace a 3 phase db in a sports pavilion. All cables are twin and Earth in the wall.
Because it's a building open to the public I decide to go with rcbos on every circuit, to give extra protection and discrimination so they don't lose everything if a fault on one circuit. Problem is price. The got someone else to qoute as well now and they have apparently decide to only put rcbos on socket circuits and 100ma rccb as main switch.

My qustion is have I over done it with rcbos on every circuit? What would you guys think?
 
It is rather difficult to comment without seeing the complete set up.

But for a start why don't you tell us why you think every circuit needs rcd protection?
 
Hi dave,
well my main thinking was the fact that all cables are installed in the walls with no mechanical protection. And well gives then extra protection with it being a public pavilion.
 
Hi dave,
well my main thinking was the fact that all cables are installed in the walls with no mechanical protection. And well gives then extra protection with it being a public pavilion.

Does being in a wall automatically require RCD protection then?

Extra protection for who and from what?
 
Well if I read the on site guide 3.6.1 F you would say yes. But got the big book out 522.6.6 (v) tells me otherwise. I've over done it.

Is thin site guide relevant to this installation? I don't know as I don't own one, I get along just fine using the actual regulations rather than resorting to the simplified guides.

Ultimately the answer will lie in whether maintainence works are carried out by or under the supervision of suitably competent (or whatever it's called) person(s) or if any Tom dick or Harry may be drilling in to the walls.

Do you have any idea why the other company have quoted for a 100mA RCD?
 
Well if I read the on site guide 3.6.1 F you would say yes. But got the big book out 522.6.6 (v) tells me otherwise. I've over done it.

Which issue of the regs is this from?


...I get along just fine using the actual regulations rather than resorting to the simplified guides.

Ultimately the answer will lie in whether maintainence works are carried out by or under the supervision of suitably competent (or whatever it's called) person(s) or if any Tom dick or Harry may be drilling in to the walls.

Surely this clause has been removed from the regs, so 30mA RCD protection will be required for T&E buried in walls (you have to assume <50mm unless there's evidence to the contrary) irrespective of the type of building or who's maintaining it?
 
Surely this clause has been removed from the regs, so 30mA RCD protection will be required for T&E buried in walls (you have to assume <50mm unless there's evidence to the contrary) irrespective of the type of building or who's maintaining it?

Have they really removed it from the yellow book? What fresh nonsense is this?

I must admit I haven't concerned myself with that reg much as I haven't installed anything flush without an earthed protection for a long time.
 
Is thin site guide relevant to this installation? I don't know as I don't own one, I get along just fine using the actual regulations rather than resorting to the simplified guides.

Ultimately the answer will lie in whether maintainence works are carried out by or under the supervision of suitably competent (or whatever it's called) person(s) or if any Tom dick or Harry may be drilling in to the walls.

Do you have any idea why the other company have quoted for a 100mA RCD?

No don't know why they want to put a 100ma rcd in. It's a TNCS / PME system I thought 100ma was for socket outlets exceeding 32A.
 
30mA rcd incomer would be non-compliant, 100ma incomer not appropriate

its either rcbos all round or...........


Is there any use of three phase equiptment in the building?

if its only single phase and likely to remain so, how about three single phase boards one on each phase with dual rcd

i had to do this once, bit naff but still was much cheaper than 30 odd rcbos

just a thought!
 
30mA rcd incomer would be non-compliant, 100ma incomer not appropriate

its either rcbos all round or...........


Is there any use of three phase equiptment in the building?

if its only single phase and likely to remain so, how about three single phase boards one on each phase with dual rcd

i had to do this once, bit naff but still was much cheaper than 30 odd rcbos

just a thought!
Hello welchybo, so I'm not so far out I should just got with my gut feeling then.
 

Reply to Sports pavilion rcbos or rccb incommer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
I've just started at a new church and the electrics are bit of a shambles. I'm not going to be touching them as I'm not qualified, but one thing I...
Replies
14
Views
4K
Currently quoting for a job that needs to be done next week and working out how best to proceed, so thoughts welcome. Current situation: -->PME...
Replies
6
Views
4K
Been to look at a job this morning for a CU change, customer the type who wants to have his say on every tiny detail. He has already bought the...
Replies
44
Views
11K
Hi all , my question for your brilliant minds is (ill first set the scene) 35mm 4 core swa coming from an external supply, 16mm earth ran out to...
Replies
3
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock