Is thin site guide relevant to this installation? I don't know as I don't own one, I get along just fine using the actual regulations rather than resorting to the simplified guides.

Ultimately the answer will lie in whether maintainence works are carried out by or under the supervision of suitably competent (or whatever it's called) person(s) or if any Tom dick or Harry may be drilling in to the walls.

Do you have any idea why the other company have quoted for a 100mA RCD?

No don't know why they want to put a 100ma rcd in. It's a TNCS / PME system I thought 100ma was for socket outlets exceeding 32A.
 
30mA rcd incomer would be non-compliant, 100ma incomer not appropriate

its either rcbos all round or...........


Is there any use of three phase equiptment in the building?

if its only single phase and likely to remain so, how about three single phase boards one on each phase with dual rcd

i had to do this once, bit naff but still was much cheaper than 30 odd rcbos

just a thought!
 
30mA rcd incomer would be non-compliant, 100ma incomer not appropriate

its either rcbos all round or...........


Is there any use of three phase equiptment in the building?

if its only single phase and likely to remain so, how about three single phase boards one on each phase with dual rcd

i had to do this once, bit naff but still was much cheaper than 30 odd rcbos

just a thought!
Hello welchybo, so I'm not so far out I should just got with my gut feeling then.
 

Reply to Sports pavilion rcbos or rccb incommer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
I've just started at a new church and the electrics are bit of a shambles. I'm not going to be touching them as I'm not qualified, but one thing I...
Replies
14
Views
5K
Currently quoting for a job that needs to be done next week and working out how best to proceed, so thoughts welcome. Current situation: -->PME...
Replies
6
Views
4K
Been to look at a job this morning for a CU change, customer the type who wants to have his say on every tiny detail. He has already bought the...
Replies
44
Views
11K
Hi all , my question for your brilliant minds is (ill first set the scene) 35mm 4 core swa coming from an external supply, 16mm earth ran out to...
Replies
3
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock