Piratepete

Evening All.
Almost clear on connecting the genny to the house!
When connecting the genny it is recommended to link the neutral to earth in the socket of the connecting cable. Why? Is there any reason why the neutral to earth link shouldn't be at the back of the fixed plug on the box housing the plug and rcd?
Cheers
Pete
 
The 230VAC output from the genny is floating (normally). You have to tie one side down to earth, because the protecting RCD that you have to install won't trip if there's an earth fault.
There's a cable linking the output socket on the genny with the plug connection on the RCD box at the house. The question was about where to put the earth to neutral link. I've seen recommendations to put it at one end of the connecting cable in the output socket. What bothers me is that customers have a habit of losing cables and would probably replace it with one that has no E/N link in it.
 
The neutral link is normally placed in the socket so that the generator is returned to it's unmodified state when disconnected, you could place the link upstream and maybe label the generator to indicate this.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Standby Generators again!
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
Piratepete,
Last reply from
DurhamSparky,
Replies
4
Views
1,819

Advert

Back
Top