Hi
So I've a project coming up where I need to Move a Fuseboard which is Split On peak with One rcd for The Flat ring and off peak Storage heaters . no rcd . Its Dated 2001 so the fuseboard will need to be replaced With a split board with 2 rcd's for on peak Power and lights etc . I've a few new circuits to install too ! maybe 2 Shower circuits . The incoming is a 4 core 25mm2 SWA
I've informed by client a new Kitchen ring and cooker supply will need to be installed
Also the old part of the kitchen which is incorporated in the flat ring .....there is no separate Kitchen Ring....be re routed and rewired so it becomes a Flat ring with Kitchen ring .
My query is The Storage Units .
My initial thoughts are that a separate Fuseboard be installed for the off peak Heating with there own seperate mcb's . So Does it need to be a split RCD board Or Just one fuseboard controlled with a single rcd . ?
I'm sure I'm not the first sparks to have come across this ?
So I'd rather take advice from the men who Do it rather than write the books
See my 17th edition mind and My insurance says .......Better to be over safe .
Thoughts and advice please Ta
Silver6003
 
Last edited by a moderator:
What do you think you should do? Have you called your schemes technical support line?

I've no idea who My schemes Is . I've only seen this Job on Monday .
So I need to talk to my client to get the Provider's number and then Speak to their Technical Support
It was this course of action I really did not want to take
I came here for advice .
So it looks like that's my next avenue then ok
Thanks
 
I've no idea who My schemes Is . I've only seen this Job on Monday .
So I need to talk to my client to get the Provider's number and then Speak to their Technical Support
It was this course of action I really did not want to take
I came here for advice .
So it looks like that's my next avenue then ok
Thanks

Scheme = CPS = Competent Persons Scheme = Elecsa / NICEIC / Stroma / Napit - you are planning to do notifiable work, so surely you are a member?

Sure - but its a 2 way street - you know, give and take.
 
A separate board for off peak sounds like a good plan.
For a single RCD on this board you would loose all heating in the flat on a single fault which could be very uncomfortable.
As it is a flat and so presumably only a few heaters, an all RCBO board may be the easiest (but not cheapest) answer.
If there are lots of heaters then a split load board with the heaters from adjacent areas on different RCDs might be better.
Ensure there is double pole switching on all the heaters so they can be separated from the circuit.
 
A separate board for off peak sounds like a good plan.
For a single RCD on this board you would loose all heating in the flat on a single fault which could be very uncomfortable.
As it is a flat and so presumably only a few heaters, an all RCBO board may be the easiest (but not cheapest) answer.
If there are lots of heaters then a split load board with the heaters from adjacent areas on different RCDs might be better.
Ensure there is double pole switching on all the heaters so they can be separated from the circuit.


Yep That's what I was thinking
A board with seperate RCBO's
I know its not going to be cheap but hey I've a good relationship with a Store Manager who works for the Sponsor !!!.
Always pays to get on with a big store manager I think
People skills half the way to get on in business
Thanks for your advice
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Storage Heaters and Consumer units with Split RCD.s
Prefix
N/A
Forum
Solar Thermal Advice Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Silver6003,
Last reply from
Silver6003,
Replies
5
Views
9,287

Advert

Back
Top