Octopus
What earthing does your property have ?
If its TNCS then it would explain why the ELI is high.Thatl be a loose neutral somewhere nearby then id have thought
I don't think there's any evidence it's a CNE fault, I would expect it to be the line connection that is high-resistance. The EFLI will be bad, the voltage will vary, but there won't be any other symptoms like tingles off things.Tenner says it's a bad neutral connection in the tee off joint under the pavement.