May be they don't have a wander lead or don't realise what a time saver it can be in such situations.
or just wanderin about...They must be wandering about it though!
Sounds to me like you have the feed t+e cable out crossed with the switch t+e cable and the strange voltage is coming through the lamp. Does the strange voltage disappear if the lamp is emoved from the fitting?
well then they get a bit of 1.0 flat twin....do an end to end on it...null it out...and use that....1 end grabbed in the croc...the other end they terminate....a more time consumin way of doin it i know....May be they don't have a wander lead or don't realise what a time saver it can be in such situations.
well then they get a bit of 1.0 flat twin....do an end to end on it...null it out...and use that....1 end grabbed in the croc...the other end they terminate....a more time consumin way of doin it i know....
but why can`t some folk think on their feet...