Stupid question? Re. Insulation resistance

Discuss Stupid question? Re. Insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

I'm talking about the real world too, it's just a simple network of five resistances in parallel. It could be five circuits with 250megohm each, or any other combination of resistances which totals 50

Are you absolutely sure about this Dave ? If each circuit had a I.R. of 250 Megohms I think that's what you'd see on the 'Global' test....
 
Remember that for any set of resistances in parallel the total resistance will be lower than the lowest value of any of the individual resistances.
The worst case scenario is when they are all equal as Davesparks has said.

e.g. if you had five circuits with very high insulation resistance and one circuit with an IR of 2MΩ, then the total resistance when measured as a "whole installation" would be less than 2MΩ.
Say the high values were all 200MΩ then the 1/r for each circuit would be 0.005 (so a total of 0.025 for five circuits) but the 2MΩ 1/r value would be 0.5 therefore the contribution of the "high" values is very small and the total resistance would work out to (1/0.525) or 1.9MΩ.
 
I don't doubt you're all correct but we're talking about insulation resistance or integrity so maintain that if every circuit [4 circuits for example] IR tested say >200 Megohms you'd also see similar as a 'global' reading.
 
I don't doubt you're all correct but we're talking about insulation resistance or integrity so maintain that if every circuit [4 circuits for example] IR tested say >200 Megohms you'd also see similar as a 'global' reading.

Taking your example, if 4 circuits measured individually at >200MOhms it is possible that a global reading would also read the same if the actual readings were very high.
But also possibly not. If all 4 circuits measured 299MOhms then the global reading would be around 75MOhms for example.
 
e.g. if you had five circuits with very high insulation resistance and one circuit with an IR of 2MΩ, then the total resistance when measured as a "whole installation" would be less than 2MΩ.
Does that mean the lowest IR reading the OP would get if he measured the 5 circuits separately would be 50MΩ ?
Sorry confused.com
 
I don't doubt you're all correct but we're talking about insulation resistance or integrity so maintain that if every circuit [4 circuits for example] IR tested say >200 Megohms you'd also see similar as a 'global' reading.

Insulation resistance is the same as any other resistance and follows the scientific laws governing resistance.
Getting a result which displays on a meter as >200megOhm just indicates that the resistance is higher than the maximum reading that instrument is capable of, an instrument with a greater scale would return an actual value for it.
You may very well get a global test result the same as each individual circuit, but that could be that the global result is actually 201megOhm and the individual circuits are all 1005megOhm
 

Reply to Stupid question? Re. Insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock