I’ve recently run a supply to a garage and I had a question concerning the earthing. Here is the situation:

TT supply to house.
Supply goes into a time-delay 100mA RCD before it splits.
This then goes through a sub-mains isolator at the house.
3-core SWA runs about 60 metres to garage.
17[SUP]th[/SUP] edition consumer unit in the garage.
New earth spike installed for supply at the garage.

So, my question: Should the SWA section be connected to earth at both ends, or only at one? Is there a reason I would NOT want to connect the earth at both ends?
 
i would connect at both ends. that way the connection between the 2 rods should bring the Ze of both down.
 
didn't spot that. isolator need to be fused to protect the SWA.
 
no, the 60898is fine. it's just in your post 1 you didn't mention overcurrent protection for the SWA.
 
Hi
As it's a TT system at origin no problem connecting SWA earth at both ends, as mentioned before would help your earthing value. But if your origin earth was PME for example, then the SWA wire from origin should be earthed but not be connected to the consumer unit in the Garage, that should be earth free of PME, then the earthing arrangment for the Garage would become TT from the earth electrode allready installed.
 
Hi
As it's a TT system at origin no problem connecting SWA earth at both ends, as mentioned before would help your earthing value. But if your origin earth was PME for example, then the SWA wire from origin should be earthed but not be connected to the consumer unit in the Garage, that should be earth free of PME, then the earthing arrangment for the Garage would become TT from the earth electrode allready installed.
why??? what's wrong with the PME in the garage?
 
Nothing in princible, but the example above, running 60 meters and a new consumer unit to a garage could require a bond to a water supply or any other extraneous conductive parts therfore that could introduce a potential back into the PME zone. If the cable was 3 core 10mm then bonding requirments for 100amp PME supply would be ok
 

Reply to Sub-mains earthing question in the Australia area at ElectriciansForums.net

Similar Threads

Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Replies
3
Views
750
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
504
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock