Hi all,
Just having a chat with a customer who we do regular maintenance work for. They have had an extension and got another company in to do the electrics due to us not having the time. The main reason for the post is the installer has used self tapping screws on all the swa glands. Is there a specific section in the regs that states swa glands must have a bolt and flying lead to the earth bar that anyone has come across?
There are a few more issues with the install like 200A MCCB for the 4C 35mm swa they have put in as well but that's under control.
Cheers.
Just having a chat with a customer who we do regular maintenance work for. They have had an extension and got another company in to do the electrics due to us not having the time. The main reason for the post is the installer has used self tapping screws on all the swa glands. Is there a specific section in the regs that states swa glands must have a bolt and flying lead to the earth bar that anyone has come across?